Posted: 2021-07-01 04:39 AM
This was originally posted on APC forums on 11/13/2013
I have reviewed the logs on the Powerchute and we are receiving numerous email alerts with regards to insufficient runtime. Everything seems to be fine in the software
not sure what is causing this problem please assist. The Risk Assessment is showing problems with the Runtime, Battery Age = 9.2, UPS Age = 9.2 and Application Shutdown
Any suggestions or recommendations?
Posted: 2021-07-01 04:39 AM
This was originally posted on APC forums on 11/14/2013
Bill thank you I will try this and let you know. I will also look at the other informational links you sent me.
Posted: 2021-07-01 04:39 AM
This reply was originally posted by Bill on APC forums on 11/13/2013
Hi,
Insufficient runtime means the UPS has insufficient battery power available to support the load for the amount of time set for Low Runtime Remaining. You need to decrease the Low Runtime Remaining threshold, decrease the load, or it could be cause by a battery that needs replacement. Since the battery / batteries are 9 plus years old I would start there. To test the battery unplug any computer equipment that is attached and plug in a lamp. Depending on the UPS model I would test with a 100 watt incandescent bulb. With the lamp on unplug the UPS for the AC source and time how long the lamp stays powered on then check the UPS runtime chart on APC.com to compare data. If the lamp shuts down quickly then the battery need to be replaced.
The Low Runtime Remaining threshold can be found in the web interface under Server Shutdown - Shutdown Settings then click Configure to see the page below. In a web browser running on the system that PowerChute Agent is installed enter https://127.0.0.1:6547
If you would like more information on insufficient runtime and Application Shutdown please review the help files. You can search on runtime and or shutdown sequence.
Posted: 2021-07-01 04:39 AM
This was originally posted on APC forums on 11/14/2013
Bill thank you I will try this and let you know. I will also look at the other informational links you sent me.