No power to/from SURT5000XLI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • No power to/from SURT5000XLI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
134
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:02 AM . Last Modified: β€Ž2024-03-08 01:40 AM

0 Likes
3
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:02 AM . Last Modified: β€Ž2024-03-08 01:40 AM

No power to/from SURT5000XLI

We've just had a pair of these units hard wired to the main supply. Before that they were sitting idle - exactly how long I couldn't say, but my guess is that it was a very long time, as the batteries appear completely dead. No sign of life anywhere. Pressing and holding the power button does nothing.
Power to the unit has been tested and verified.

This prompts two questions:
1. Is it not possible to power up these units on bypass, even if the batteries are shot?
2. Is there any way to test the circuitry of the device before I shell out $1000 on new batteries and find the devices themselves are dead.

Thanks

Andy

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • dead
  • surt5000xli
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:02 AM . Last Modified: β€Ž2024-03-08 01:40 AM

0 Likes
0
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:02 AM . Last Modified: β€Ž2024-03-08 01:40 AM

Yes, it's possible, but this isn't something you should carry out on your own as it's extremely dangerous. In the US OSHA probably don't even allow untrained personnel to carry it out. Similar things probably apply in UK.

The SURT5000XLI is powered by RBC44, which consists of 16 12v 5Ah batteries connected in series with nominal voltage of 192v and operating voltage of around 220v DC. You'd need to apply around 200v DC with a DC power supply.

Find a UPS service/maintenance company. They should be able to come to your site and perform the test with a power supply,then after verifying the functionality, rebuild your batteries with 12v 5Ah batteries preserving your old hardware, take your old batteries and furnish the proper certificate showing lawful disposal of spent batteries.


-KVAr(Not an APC Affiliate ), my posts do not reflect the opinion of APC-MGE.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:02 AM . Last Modified: β€Ž2024-03-08 01:40 AM

0 Likes
0
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:02 AM . Last Modified: β€Ž2024-03-08 01:40 AM

Many thanks for the advice (and warning). In an effort to stay unfried, I have made arrangement for replacement batteries. Safest all round πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: β€Ž2021-06-30 06:02 AM . Last Modified: β€Ž2024-03-08 01:40 AM

0 Likes
0
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:02 AM . Last Modified: β€Ž2024-03-08 01:40 AM

Unfortunately, the unit does require good batteries to turn on. The only way that APC would support testing the system is to have you puchase new batteries. I see this quite often as units sit around for quite some time before being used in some circumstances.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:02 AM . Last Modified: β€Ž2024-03-08 01:40 AM

0 Likes
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:02 AM . Last Modified: β€Ž2024-03-08 01:40 AM

Yes, it's possible, but this isn't something you should carry out on your own as it's extremely dangerous. In the US OSHA probably don't even allow untrained personnel to carry it out. Similar things probably apply in UK.

The SURT5000XLI is powered by RBC44, which consists of 16 12v 5Ah batteries connected in series with nominal voltage of 192v and operating voltage of around 220v DC. You'd need to apply around 200v DC with a DC power supply.

Find a UPS service/maintenance company. They should be able to come to your site and perform the test with a power supply,then after verifying the functionality, rebuild your batteries with 12v 5Ah batteries preserving your old hardware, take your old batteries and furnish the proper certificate showing lawful disposal of spent batteries.


-KVAr(Not an APC Affiliate ), my posts do not reflect the opinion of APC-MGE.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore