No batteries installed but battery capacity 100%

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • No batteries installed but battery capacity 100%
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
6
2231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

No batteries installed but battery capacity 100%

Hi.

I have an APC Smart-UPS RT 10000 RM XL and on the telnet console I see this error:

Status of UPS : On Line, No batteries installed, No Other Alarms Present

But on the same console I see battery capacity 100 and runtine remaining 24 min.

The audible alarm (beep) is on and I did not manage in turning it off even from Configuration-General-Audible Alarm: off.

This is the console status:

------- Smart-UPS RT 10000 RM XL ----------------------------------------------
        Status of UPS : On Line, No batteries installed, No Other Alarms Present
        Last Transfer : Due to software command or UPS's test control
        -----------------------------------------------------------------------
        Input Voltage    : 237.6 VAC         Input Frequency     : 49.98 Hz
        Output Voltage   : 230.4 VAC         Output Frequency    : 49.98 Hz
        Load Power       : 012.0 % Watts     Battery Voltage     : 218.1 VDC
        Max Line Voltage : 241.9 VAC         Battery Capacity    : 100.0 %
        Min Line Voltage : 234.7 VAC         Runtime Remaining   : 0024 min
                                             Apparent Load Power : 013.0 % VA
        Internal Temp    : 022.9 C
        -----------------------------------------------------------------------
        Self-Test Result : Not available     Calibration Result  : Not available
        Self-Test Date   : 01/20/2015        Calibration Date    : Unknown

The front panel of the UPS shows the "replace battery" red LED flashing and no information about battery remaining runtime and load.

Could you help me to solve the problem, please?

Thank you very much! Bye.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • fault
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:25 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
2230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:25 PM . Last Modified: ‎2024-03-19 12:09 AM

Thank you Angela for your answer.

No, the UPS does not support any load and it switches off if putted on battery.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
2230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

Hi,

Can you clarify how old the batteries are or navigate the menu in the Telnet console to see what it says for the last battery replacement date?

Also, if possible, the config.ini, event.txt, and data.txt log files would be extremely helpful and should answer that question too. Instructions on doing that are here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 and it looks like you have an NMC1 in your UPS so you'll want to use FTP (or SCP).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
2230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

Hi Angela, thank you very much for your answer.

On 1/21/2015 2:28 PM, Angela said:

Can you clarify how old the batteries are or navigate the menu in the Telnet console to see what it says for the last battery replacement date?

The batteries (and the entire UPS) are 4,5 years old.

On 1/21/2015 2:28 PM, Angela said:

Also, if possible, the config.ini, event.txt, and data.txt log files would be extremely helpful and should answer that question too

I'm trying to  download these files using FTP. Thelogin  works, but the file transfer not. I'm trying and trying but when I download one of these three files I get the " 421 Service not available, closing control connection." error.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
2230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

OK, since the batteries are older,  they very well could have a  "good" voltage but not actually be holding their capacity. Good voltage does not necessarily mean the batteries are  good.

On the FTP issue, this usually means your FTP data port is blocked.  I have had this issue before and found my VPN  service to be the culprit.  Worst case, can you access the web interface and go to the event and data log and press "launch log in new window" and copy/paste what you see there into a file of some sort?

My gut tells me that it is likely time to start preparing for replacing all of your batteries due to the age and the issue you're seeing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
2231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

On 1/26/2015 4:06 PM, Angela said:

OK, since the batteries are older,  they very well could have a  "good" voltage but not actually be holding their capacity. Good voltage does not necessarily mean the batteries are  good.

But what about the "Battery Disconnected" error? I manually checked the batteries and they are not disconnected from the main unit.

On 1/26/2015 4:06 PM, Angela said:

can you access the web interface and go to the event and data log and press "launch log in new window" and copy/paste what you see there into a file of some sort?

Event log:

Date Time Event
Date Time Event
01/30/2015 12:30:03 System: Web user 'apc' logged in from 192.168.33.140.
01/30/2015 09:19:19 System: Network service started. System IP is 192.168.33.20 from DHCP server 192.168.33.1 with 43200 second lease.
01/30/2015 09:19:19 System: Configuration change. DHCP lease2 time.
01/30/2015 09:19:19 System: Configuration change. DHCP lease1 time.
01/30/2015 09:19:19 System: Configuration change. DHCP lease date.
01/30/2015 03:50:51 System: Network service started. System IP is 192.168.33.20 from DHCP server 192.168.33.1 with 43200 second lease.
01/30/2015 03:50:51 System: Configuration change. DHCP lease2 time.
01/30/2015 03:50:51 System: Configuration change. DHCP lease1 time.
01/30/2015 03:50:51 System: Configuration change. DHCP lease date.
01/29/2015 21:58:46 System: Network service started. System IP is 192.168.33.20 from DHCP server 192.168.33.1 with 43200 second lease.
01/29/2015 21:58:46 System: Configuration change. DHCP lease2 time.
01/29/2015 21:58:46 System: Configuration change. DHCP lease1 time.
01/29/2015 21:58:46 System: Configuration change. DHCP lease date.
01/29/2015 16:43:10 System: Network service started. System IP is 192.168.33.20 from DHCP server 192.168.33.1 with 43200 second lease.
01/29/2015 16:43:10 System: Configuration change. DHCP lease2 time.
01/29/2015 16:43:10 System: Configuration change. DHCP lease1 time.
01/29/2015 16:43:10 System: Configuration change. DHCP lease date.
01/29/2015 11:07:28 System: Network service started. System IP is 192.168.33.20 from DHCP server 192.168.33.1 with 43200 second lease.
01/29/2015 11:07:28 System: Configuration change. DHCP lease2 time.
01/29/2015 11:07:28 System: Configuration change. DHCP lease1 time.
01/29/2015 11:07:28 System: Configuration change. DHCP lease date.
01/29/2015 05:34:42 System: Network service started. System IP is 192.168.33.20 from DHCP server 192.168.33.1 with 43200 second lease.
01/29/2015 05:34:41 System: Configuration change. DHCP lease2 time.
01/29/2015 05:34:41 System: Configuration change. DHCP lease1 time.
01/29/2015 05:34:41 System: Configuration change. DHCP lease date.
01/29/2015 00:00:18 System: Network service started. System IP is 192.168.33.20 from DHCP server 192.168.33.1 with 43200 second lease.
01/29/2015 00:00:18 System: Configuration change. DHCP lease2 time.
01/29/2015 00:00:18 System: Configuration change. DHCP lease1 time.
01/29/2015 00:00:18 System: Configuration change. DHCP lease date.
01/28/2015 18:44:42 System: Network service started. System IP is 192.168.33.20 from DHCP server 192.168.33.1 with 43200 second lease.
01/28/2015 18:44:42 System: Configuration change. DHCP lease2 time.
01/28/2015 18:44:42 System: Configuration change. DHCP lease1 time.
01/28/2015 18:44:42 System: Configuration change. DHCP lease date.
01/28/2015 13:17:21 System: Network service started. System IP is 192.168.33.20 from DHCP server 192.168.33.1 with 43200 second lease.
01/28/2015 13:17:21 System: Configuration change. DHCP lease2 time.
01/28/2015 13:17:21 System: Configuration change. DHCP lease1 time.
01/28/2015 13:17:21 System: Configuration change. DHCP lease date.

Data log:

  Smart-UPS RT 10000 RM XL Integrated EMU
Date  Time  Vmin  Vmax  Vout  Iout  %Wout  Freq  %Cap  Vbat  TupsC  %VAout  TIambC  %HumI 
  Smart-UPS RT 10000 RM XL Integrated EMU
Date  Time  Vmin  Vmax  Vout  Iout  %Wout  Freq  %Cap  Vbat  TupsC  %VAout  TIambC  %HumI 
 01/30/2015   12:24:06   233.2   237.6   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   22.0     
 01/30/2015   12:14:06   233.2   241.9   0.0   0.00   0.0   0.00   100.0   191.1   19.0   0.0   22.0     
 01/30/2015   12:04:06   234.7   240.4   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   22.0     
 01/30/2015   11:54:06   237.6   240.4   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   22.0     
 01/30/2015   11:44:06   234.7   240.4   0.0   0.00   0.0   0.00   100.0   216.0   19.0   0.0   22.0     
 01/30/2015   11:34:06   234.7   240.4   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   22.0     
 01/30/2015   11:24:06   236.1   239.0   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   22.0     
 01/30/2015   11:14:06   236.1   239.0   0.0   0.00   0.0   0.00   100.0   217.0   19.0   0.0   22.0     
 01/30/2015   11:04:06   236.1   240.4   0.0   0.00   0.0   0.00   100.0   216.0   19.0   0.0   22.0     
 01/30/2015   10:54:06   234.7   240.4   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   22.0     
 01/30/2015   10:44:06   233.2   240.4   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   23.0     
 01/30/2015   10:34:06   230.4   237.6   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   22.0     
 01/30/2015   10:24:06   231.8   236.1   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   23.0     
 01/30/2015   10:14:06   231.8   239.0   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   23.0     
 01/30/2015   10:04:06   236.1   241.9   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   23.0     
 01/30/2015   09:54:06   231.8   240.4   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   23.0     
 01/30/2015   09:44:06   231.8   237.6   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   23.0     
 01/30/2015   09:34:06   230.4   237.6   0.0   0.00   0.0   0.00   100.0   217.0   19.0   0.0   23.0     
 01/30/2015   09:24:06   230.4   234.7   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   23.0     
 01/30/2015   09:14:06   231.8   237.6   0.0   0.00   0.0   0.00   100.0   218.1   19.0   0.0   23.0     
 01/30/2015   09:04:06   231.8   237.6   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   23.0     
 01/30/2015   08:54:06   231.8   236.1   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   22.0     
 01/30/2015   08:44:06   233.2   237.6   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   23.0     
 01/30/2015   08:34:06   233.2   237.6   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   23.0     
 01/30/2015   08:24:06   228.9   236.1   0.0   0.00   0.0   0.00   100.0   217.0   18.4   0.0   23.0     
 01/30/2015   08:14:06   230.4   236.1   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   22.0     
 01/30/2015   08:04:06   230.4   236.1   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   22.0     
 01/30/2015   07:54:06   230.4   236.1   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   22.0     
 01/30/2015   07:44:06   233.2   240.4   0.0   0.00   0.0   0.00   100.0   155.5   18.4   0.0   22.0     
 01/30/2015   07:34:06   230.4   237.6   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   22.0     
 01/30/2015   07:24:06   227.5   233.2   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   22.0     
 01/30/2015   07:14:06   226.0   233.2   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   22.0     
 01/30/2015   07:04:06   221.7   228.9   0.0   0.00   0.0   0.00   100.0   218.1   18.4   0.0   22.0     
 01/30/2015   06:54:06   226.0   230.4   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   06:44:06   226.0   228.9   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   06:34:06   224.6   233.2   0.0   0.00   0.0   0.00   100.0   216.0   17.9   0.0   22.0     
 01/30/2015   06:24:06   227.5   234.7   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   06:14:06   226.0   231.8   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   06:04:06   228.9   237.6   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   05:54:06   233.2   237.6   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   05:44:06   231.8   237.6   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   05:34:06   233.2   237.6   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   05:24:06   231.8   237.6   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   05:14:06   231.8   237.6   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   05:04:06   233.2   239.0   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   04:54:06   234.7   239.0   0.0   0.00   0.0   0.00   100.0   216.0   17.9   0.0   22.0     
 01/30/2015   04:44:06   231.8   239.0   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     
 01/30/2015   04:34:06   233.2   239.0   0.0   0.00   0.0   0.00   100.0   218.1   17.9   0.0   22.0     

Please note that the UPS is actually switched off, to shutdown the audible alarm.

On 1/26/2015 4:06 PM, Angela said:

My gut tells me that it is likely time to start preparing for replacing all of your batteries due to the age and the issue you're seeing.

I know the batteries should be replaced. But are you sure that it is not a problem on the internal unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
2231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

I can't be sure it is not a problem with the unit based on what I am seeing. Does the UPS support a load if you test it and put it on battery even though it says the battery is disconnected? Good battery voltage/capacity does not necessarily mean the battery is "good." I don't see anything else reported by the UPS, like a charger fault, but the first thing I'd do is if you had spare batteries would be to try them. Otherwise, it could be the unit or batteries but batteries could be a good first try in troubleshooting before deeming the unit faulty - based on the age and behavior I am seeing. I don't want to tell you with 100% certainty that it is batteries and go out and purchase them and find out the UPS has a problem but I am just giving you educated feedback based on what I see here.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:25 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
2231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:25 PM . Last Modified: ‎2024-03-19 12:09 AM

Thank you Angela for your answer.

No, the UPS does not support any load and it switches off if putted on battery.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore