Hi,
I have an apc 9631, it was on old firmware ,when i update it the webpage it says "no ups found".
My UPS : SURTD5000XLI
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:24 PM . Last Modified: 2024-02-14 11:56 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:24 PM . Last Modified: 2024-02-14 11:56 PM
Thanks Matt ( Problem Solved )
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:24 PM . Last Modified: 2024-02-14 11:56 PM
Hi Sherk
It looks like you have upgraded the NMC firmware with the one for the 3 Phase Symmetra rather than for the Smart UPS UPS.
Her is the firmware you need.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:24 PM . Last Modified: 2024-02-14 11:56 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:24 PM . Last Modified: 2024-02-14 11:56 PM
Thanks Matt ( Problem Solved )