No PCNS,low battery time, according event.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • No PCNS,low battery time, according event.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
1
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

No PCNS,low battery time, according event.

Hello,

sorry in upfront. I know that the web is full of discussions and question about what is low battery condition and so on.

First of all, I don't want to use PCNS or whatever SW on the clients. We have LX clients and have configured SNMP Traps on them.

Basically all we want to do is to receive a notification for the "last 10 Battery Minutes" and from there decide our self in which order or how

the shutdown happens.

I did some basic test. I attached some load (not shutdown able... beamer)  to the battery and removed the input power. 

I watched all the emails flow in. The amount of repetition is because of the "repeat" setting in the Events setting.

So here they are:

50xUPS: On battery power in response to rapid change of input.

8x: Critical - UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.

1x: Warning - UPS: Main outlet group, UPS Outlets, has been commanded to shutdown with on delay.

1x Warning - UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown, sequenced.

1x Informational - UPS: No longer on battery power.

1x Informational - UPS: The graceful shutdown period has ended.

4x Informational - UPS: A low battery condition no longer exists

5x Warning - UPS: The power for the main outlet group, UPS Outlets, is now turned off.

5x Critical - UPS: The output power is turned off.

5x Critical - UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

5x Warning - UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.

For all what I have read now in the forums / web I would assume that

"Critical - UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon."

is the indication for my desired "last 10 minutes" Battery Power.

Now the mystery begins. I did this test two times. One time with the default setting of 2 minutes "Low Battery duration", and one time with 10 minutes "Low Battery duration"

For both tests I can see that

"Critical - UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon."

comes appr. 10 minutes before 

"Warning - UPS: Main outlet group, UPS Outlets, has been commanded to shutdown with on delay."

11/12/2015 15:39:44 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
11/12/2015 15:39:44 Device UPS: A low battery condition no longer exists.
11/12/2015 15:39:44 Device UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
11/12/2015 15:39:43 Device UPS: The output power is turned off.
11/12/2015 15:39:43 Device UPS: The graceful shutdown period has ended.
11/12/2015 15:39:43 Device UPS: No longer on battery power.
11/12/2015 15:39:43 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown, sequenced.
11/12/2015 15:39:43 Device UPS: Main outlet group, UPS Outlets, has been commanded to shutdown with on delay.
11/12/2015 15:39:43 Device UPS: The power for the main outlet group, UPS Outlets, is now turned off.
11/12/2015 15:30:19 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/12/2015 15:30:05 Device UPS: A low battery condition no longer exists.
11/12/2015 15:29:23 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/12/2015 15:29:21 Device UPS: A low battery condition no longer exists.
11/12/2015 15:29:19 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/12/2015 15:29:18 Device UPS: A low battery condition no longer exists.
11/12/2015 15:29:13 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/12/2015 14:00:25 Device UPS: On battery power in response to rapid change of input.

Another:

10/19/2015 14:10:27 Device UPS: A discharged battery condition no longer exists.
10/19/2015 13:54:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
10/19/2015 13:54:34 Device UPS: The power for the main outlet group, UPS Outlets, is now turned on.
10/19/2015 13:54:33 Device UPS: The output power is now turned on.
10/19/2015 13:46:59 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
10/19/2015 13:46:58 Device UPS: A low battery condition no longer exists.
10/19/2015 13:46:58 Device UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
10/19/2015 13:46:57 Device UPS: The output power is turned off.
10/19/2015 13:46:57 Device UPS: The graceful shutdown period has ended.
10/19/2015 13:46:57 Device UPS: No longer on battery power.
10/19/2015 13:46:57 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown, sequenced.
10/19/2015 13:46:57 Device UPS: Main outlet group, UPS Outlets, has been commanded to shutdown with on delay.
10/19/2015 13:46:57 Device UPS: The power for the main outlet group, UPS Outlets, is now turned off.
10/19/2015 13:38:00 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
10/19/2015 13:37:55 Device UPS: A low battery condition no longer exists.
10/19/2015 13:37:51 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
10/19/2015 13:37:49 Device UPS: A low battery condition no longer exists.
10/19/2015 13:37:46 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
10/19/2015 09:49:08 Device UPS: On battery power in response to distorted input.

1.) Please confirm if "Device UPS: The battery power is too low to continue to support the load;" is the indication for the "low battery duration"

2.) Why did I get two times 10 minutes ? 

3.) What is the Event of the "real" shutdown of the UPS Outputs, without any delays etc.. e.g. " is now turned off. " ? 

4.) What means "Device UPS: A low battery condition no longer exists. " I don't understand  why this shows up. Why is the low battery condition over ?

Thanks for your comments.

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

i added the data log here:

Smart-UPS 2200
Date Time Vmin Vmax Vout Iout %Wout %out FrqOut %Cap Vbat Tups
11/12/2015 15:42:14 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 46.44 27.00
11/12/2015 15:37:14 0.00 0.00 229.59 1.81 18.19 18.80 50.00 5.00 44.00 27.00
11/12/2015 15:32:14 0.00 0.00 231.00 2.00 18.80 20.80 50.00 11.00 45.06 26.50
11/12/2015 15:27:14 0.00 0.00 231.00 2.06 19.50 21.39 50.00 16.00 45.88 26.09
11/12/2015 15:22:14 0.00 0.00 231.00 2.16 19.50 22.09 50.00 20.00 46.44 25.59
11/12/2015 15:17:14 0.00 0.00 231.00 1.50 16.19 15.59 50.00 24.00 46.97 25.19
11/12/2015 15:12:14 0.00 0.00 229.59 2.22 20.09 22.69 50.00 28.00 47.25 25.19
11/12/2015 15:07:14 0.00 0.00 229.59 2.22 20.09 23.39 50.00 32.00 47.50 24.69
11/12/2015 15:02:14 0.00 0.00 229.59 2.22 20.09 23.39 50.00 36.00 47.78 24.30
11/12/2015 14:57:14 0.00 0.00 229.59 2.22 19.50 23.39 50.00 41.00 48.03 23.80
11/12/2015 14:52:14 0.00 0.00 231.00 2.22 20.09 23.39 50.00 46.00 48.31 23.39
11/12/2015 14:47:14 0.00 0.00 228.30 1.81 14.89 18.80 50.00 51.00 48.84 22.50
11/12/2015 14:42:14 0.00 0.00 231.00 1.81 14.89 18.80 50.00 56.00 48.84 22.00
11/12/2015 14:37:14 0.00 0.00 231.00 1.81 14.89 18.80 50.00 58.00 49.13 21.59
11/12/2015 14:32:14 0.00 0.00 228.30 1.81 14.30 18.80 50.00 63.00 49.41 21.09
11/12/2015 14:27:14 0.00 0.00 229.59 1.81 14.30 18.80 50.00 67.00 49.41 20.19
11/12/2015 14:22:14 0.00 0.00 229.59 1.81 14.89 18.80 50.00 72.00 49.66 19.80
11/12/2015 14:17:14 0.00 0.00 228.30 1.81 14.89 18.80 50.00 76.00 49.66 19.30
11/12/2015 14:12:14 0.00 0.00 228.30 1.81 14.30 18.80 50.00 81.00 49.94 18.89
11/12/2015 14:07:14 0.00 0.00 228.30 1.81 14.89 18.80 50.00 85.00 49.94 18.00
11/12/2015 14:02:14 0.00 236.09 229.59 1.81 14.89 18.80 50.00 86.00 49.66 18.00
11/12/2015 13:57:14 236.09 236.09 236.09 0.44 5.19 5.00 49.97 100.00 54.53 17.50
11/12/2015 13:52:14 234.69 236.09 236.09 1.91 21.39 20.09 49.97 100.00 54.53 17.50
11/12/2015 13:47:14 234.69 236.09 236.09 1.81 21.39 19.50 49.97 100.00 54.53 17.50

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

i added the data log here:

Smart-UPS 2200
Date Time Vmin Vmax Vout Iout %Wout %out FrqOut %Cap Vbat Tups
11/12/2015 15:42:14 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 46.44 27.00
11/12/2015 15:37:14 0.00 0.00 229.59 1.81 18.19 18.80 50.00 5.00 44.00 27.00
11/12/2015 15:32:14 0.00 0.00 231.00 2.00 18.80 20.80 50.00 11.00 45.06 26.50
11/12/2015 15:27:14 0.00 0.00 231.00 2.06 19.50 21.39 50.00 16.00 45.88 26.09
11/12/2015 15:22:14 0.00 0.00 231.00 2.16 19.50 22.09 50.00 20.00 46.44 25.59
11/12/2015 15:17:14 0.00 0.00 231.00 1.50 16.19 15.59 50.00 24.00 46.97 25.19
11/12/2015 15:12:14 0.00 0.00 229.59 2.22 20.09 22.69 50.00 28.00 47.25 25.19
11/12/2015 15:07:14 0.00 0.00 229.59 2.22 20.09 23.39 50.00 32.00 47.50 24.69
11/12/2015 15:02:14 0.00 0.00 229.59 2.22 20.09 23.39 50.00 36.00 47.78 24.30
11/12/2015 14:57:14 0.00 0.00 229.59 2.22 19.50 23.39 50.00 41.00 48.03 23.80
11/12/2015 14:52:14 0.00 0.00 231.00 2.22 20.09 23.39 50.00 46.00 48.31 23.39
11/12/2015 14:47:14 0.00 0.00 228.30 1.81 14.89 18.80 50.00 51.00 48.84 22.50
11/12/2015 14:42:14 0.00 0.00 231.00 1.81 14.89 18.80 50.00 56.00 48.84 22.00
11/12/2015 14:37:14 0.00 0.00 231.00 1.81 14.89 18.80 50.00 58.00 49.13 21.59
11/12/2015 14:32:14 0.00 0.00 228.30 1.81 14.30 18.80 50.00 63.00 49.41 21.09
11/12/2015 14:27:14 0.00 0.00 229.59 1.81 14.30 18.80 50.00 67.00 49.41 20.19
11/12/2015 14:22:14 0.00 0.00 229.59 1.81 14.89 18.80 50.00 72.00 49.66 19.80
11/12/2015 14:17:14 0.00 0.00 228.30 1.81 14.89 18.80 50.00 76.00 49.66 19.30
11/12/2015 14:12:14 0.00 0.00 228.30 1.81 14.30 18.80 50.00 81.00 49.94 18.89
11/12/2015 14:07:14 0.00 0.00 228.30 1.81 14.89 18.80 50.00 85.00 49.94 18.00
11/12/2015 14:02:14 0.00 236.09 229.59 1.81 14.89 18.80 50.00 86.00 49.66 18.00
11/12/2015 13:57:14 236.09 236.09 236.09 0.44 5.19 5.00 49.97 100.00 54.53 17.50
11/12/2015 13:52:14 234.69 236.09 236.09 1.91 21.39 20.09 49.97 100.00 54.53 17.50
11/12/2015 13:47:14 234.69 236.09 236.09 1.81 21.39 19.50 49.97 100.00 54.53 17.50

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore