AP5406 screen resolution issues with 640x320

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP5406 screen resolution issues with 640x320
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:40 PM

0 Likes
5
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:40 PM

AP5406 screen resolution issues with 640x320

I'm having some issues with my new KVM solution. The AP5017 with the 17" screen is giving me some difficulties drawing OpenVMS and Novell Netware console screen which use a low resolution. The screen fits the width fairly well, but the height of the screen is wrong. Missing is about the bottom 1/3 of the console screen. I can't shrink the vertical alignment either. I believe that the proper screen resolution is VGA (640x480) but the AP5017 is detecting it at 640x320.

Are there any hacks to make this monitor a better match for lower resolutions?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:39 PM

0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:39 PM

Hello,

Does this behaviour occur while attaching a normal monitor?

Does this only happen in console/command line screens? Can you try dropping a OS environment (like windows) down to 640x480 to see if it displays properly?

Has this ever worked? What is the serial number on the unit?

The more info the better πŸ˜‰

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:40 PM

0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:40 PM

Ok, I really gave it a serious look at today and even found a work around!

Workaround: Reboot the IP-KVM, reconnect to the server.

Note: This will fix the display for one server. If you have multiple servers under-drawing on the IP-KVM, you will need to reboot the IP-KVM and reconnect for each server. The previous servers will keep their resolution. Do not press the auto adjust button.

Environment notes: I have a 16-port IP KVM with other 16-port IP-KVM's daisy chained from the master IP-KVM/KMM.

Testing: I did try the other monitor Cap1, and learned that the screen resolution is in fact 720x400 at 31.3 KHz / 69.9 Hz. The monitor had no troubles displaying the screen correctly. I tired Windows as well, and dropped to 640x480, but had no problems with the screen. I tried the console screen on the NetWare server and a few servers worked, and a few servers did not work. Checking with the external monitor they had the resolution mentioned above, but for some odd reason the IP-KVM wouldn't match the resolution correctly on a few. I rebooted the IP-KVM and reconnected to that last server. The IP-KVM then reset the resolution and displayed the screen correctly, but only for this one server. If I pressed the auto-adjust button the IP-KVM would go back to the problem resolution. I think this is what might be causing my situation.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:40 PM

0 Likes
0
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:40 PM

When screen size mismatch occurs on lower resolution output (I.E. 720 x 400, such as text based console systems), reboot ip KVM then reconnect to the previous server.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:39 PM

0 Likes
0
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:39 PM

Does the issue exist if you connect the KMM directly to the server or only when going through the KVM.

That will help us isolate the issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:39 PM

0 Likes
0
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:39 PM

I've connected the KMM directly to the back of one of the servers and the screen issue is the same, the KMM erroneously displays the server's console screen as elongated in the vertical direction with a portion of the bottom of the screen missing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:39 PM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:52 AM . Last Modified: β€Ž2024-02-14 10:39 PM

Hello,

Does this behaviour occur while attaching a normal monitor?

Does this only happen in console/command line screens? Can you try dropping a OS environment (like windows) down to 640x480 to see if it displays properly?

Has this ever worked? What is the serial number on the unit?

The more info the better πŸ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore