ISX PDU firmware

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ISX PDU firmware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
K-Dog_apc
Lieutenant JG K-Dog_apc
Lieutenant JG

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
16
3132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:41 PM

ISX PDU firmware

I am looking for the latest XPDU firmware. 3-phase tech support e-mailed me

AOS = apc_hw02_aos_334.bin
APP = apc_hw02_xpdu_331.bin

I had read else where in these forums that there was an xpdu 3.3.3 out there. (search forum for xpdu) Could that have been a reference to an earlier version AOS?

thanx

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

Hi,

3.7.3 is the most up-to-date firmware. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 16
K-Dog_apc
Lieutenant JG K-Dog_apc
Lieutenant JG

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:41 PM

is this also true for the 4500 series brain cans too?

Message was edited by: K-Dog

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

K-dog,

That is the latest available FW for A 3-phase ISX PDU'S Network Management Card. I can't recall off the top of my head if there was anything embedded with 3.3.3, based on the numbering scheme, it wouldn't make sense that there was. The 3.x have gone 3.3.1, 3.3.4 and 3.5.7. On the APP side I believe it went 3.3.1 and 3.5.6. I will double check in the morning when I have access to my computer to check my backtracked FW versions.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

hello,

As far as I know, the firmware you got from Tech support is the latest version for xPDU. I can't remember there was xpdu 333 released.

Message was edited by: annwang

Reply

Link copied. Please paste this link to share this article on your social media post.

K-Dog_apc
Lieutenant JG K-Dog_apc
Lieutenant JG

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

Notorious & Ann

Thanks for the replies...I am interested in making sure the ISX PDUs are able to be put on the public side. The thread I saw mentioned the latest firmware fixed an issue of the ISX PDUs having to be on the private side.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

K-Dog

I have verified with APC Three-Phase support they are currently at 3.3.4. They are not yet up to the single-phase standard of 3.5.7

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

I was assuming that you are using 2nd generation PDU brain that should have the part number as OM5103/OM5104. If it is , you can put the XPDU v3.3.1 to public side . If you have ISX mgr, you can also add xPDU to ISX mgr just like adding other APC network enabled devices..

Message was edited by: annwang

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

4500 series should be the old style brain cans that did not have a built in web interface or SNMP capability. I don't think you can use the above xpdu firmware for the 1st gen xpdu brain. The old gen xpdu communicated using DCAL and could only be monitored while on the private side of an Information Controller or ISX Manager.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

Thanks

That is the right FW file.

Unfortunately the log data for each circuit is still blank.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

Sorry about bringing back an old thread but it is exactly what I am looking for.

I have 3 tower PDUs that have never been updated since install over 5 years ago.  I am looking to see output breaker readings but everything comes up empty in InfraStruXure Manager.  I figured a FW update on these 3 might start that monitoring.

The units are 3-phase 0M-5103

Application Module

Name: xpdu

Version: v3.3.1

Date: 04/17/2007

  

APC OS (AOS)

Name: aos

Version: v3.3.4

Date: 01/05/2007

Could I get a link for an update.  My ISX Manager program doesn't work well for updates since we have to use a proxy.  I think I was able to manually update the rack PDUs last time manually.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:40 PM

I'll attach the file here for you. Generally, any firmware downloads would be posted here -> Software / Firmware

I can't find that one though..

*Edit* - found it. Configurable Power Distribution Unit Firmware v3.7.3 For some reason, it does not follow the naming conventions of other downloads..

Attachments
apc_hw02_aos373_xpdu373.exe.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

cry I don't know much about that device personally and the application as to what shows and what should not show. Are you thinking they should be showing or was it a feature you were looking for? based on your first post, it seemed to be something you thought should be there and was hoping a FW update fixed it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

The devices in question are full rack height tower PDUs that feed the individual PDUs in each rack.

I can see log data on the individual rack PDUs and figure there should be log data for the larger PDUs.

We have some blade enclosures connected directly to these PDUs, I was hoping to get readings on the current to those.

1015_APC-rackpdu.png

1016_APC-xpdu.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

Hello again eziemann - I asked someone on our three phase team for help here. They explained to me that you must have Branch Circuit Monitoring boards (which is an add on) installed because they do not come installed from the factory. Here is the link to that part -> BRANCH MONITORING CIRCUIT BOARD (21 POSITIONS) . Basically for each panel, you'd need two installed - one for the evens and one for the odds per panel. The load must be taken down to install these on the ISX PDU. Once you install these devices, then the data log will populate. Right now though, there is nothing measuring the branch circuits.

The only thing you can probably see now is just that those branch circuits exist. Those are listed under Power Distribution->Branch Circuits sub tab.

Hope that helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

That would explain it.

Thanks for you help!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

It's been a few years since that firmware was recommended.  Is 3.7.3 still the most current FW?  I've got a whole bunch of 'em, and I'd like to ensure we're current.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
3131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

Hi,

3.7.3 is the most up-to-date firmware. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore