Newbie Question of APC Symmetra UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Newbie Question of APC Symmetra UPS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:06 AM . Last Modified: ‎2024-03-19 01:09 AM

0 Likes
3
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:06 AM . Last Modified: ‎2024-03-19 01:09 AM

Newbie Question of APC Symmetra UPS

Hi all,

I am new to APC Symmetra UPS and I am looking to purchase a UPS for a raised floor computer room with roughly 10 rack cabinets in total.

Total Load: 21kW
Operating Voltage: 230V
Extra power for future expansion? 30%
Run time during power failure? 1 hour
Rack mountable UPS? No
Redundant Solution? No
I entered the above criteria into the APC UPS Sizing Tool and it came back with a suggestion of:
APC Symmetra PX 32kW All-In-One, Scalable to 48kW, 400V + (1)SYCFXR48-9 Battery Unit
Part Number(s): SY32K48H-PD + SYCFXR48-9

Q1. Does it mean that SY32K48H-PD already comes with 32kW batteries and the extra SYCFXR48-9 will provide the 12kW more?
Q2. In Symmetra-PX, how many rows of batteries can the rack hold?
Generally, how much kW can one battery provide?
Q3. Apart from the above 2 part nos, what else do I need to purchase?
Someone suggested PDM1316IEC-P, what is this?
Q4. One vendor suggested SY16K48H-PD with 3 x SYBT9-B4. Is this the same solution as what the sizing tools suggested? I am a bit confused.
Q5. I intend to line up the rack cabinets and Symmetra PX UPS in a row but if I have space problem, can I install the Symmetra PX UPS away from the line of rack cabinets?

Can someone clarify that for me?
Thanks.


Thanks all.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:06 AM . Last Modified: ‎2024-03-19 01:09 AM

0 Likes
0
627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:06 AM . Last Modified: ‎2024-03-19 01:09 AM

Yes the UPS and Additional XR battery frame will take up the space of two server racks.

The UPS you are looking at has built in distribution that requires the prefabricated breaker and cordset module. This module clips into place inside the UPS to allow easily configurable distribution. The one you have been quoted has 3 whips each is a 3 Wire 32A IEC309 and the lenghts are 300cm, 360cm, 420cm.

I believe the UPS you are looking into can support up to 6 of these distribution modules. However you still have to stay within your load levels as you can add to many modules and load which would result in overloading the UPS.

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=PDM1332IEC-3P

As far as a Maintenance Bypass system. I think this should always be included if your load cannot be shut down for maintenance activities. Most maintenance actions can be performed on the UPS with it online however there are certain conditions that would require you to either be able to place the system into maintenance bypass or shutdown the load. I'm not very familiar with your regions Bypass enclosures and if there are currently and wall mount options however the full size unit with additional distribution is the:

http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=PDRPPH2000-M

This will also take up an additional amount of rack space.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:06 AM . Last Modified: ‎2024-03-19 01:09 AM

0 Likes
0
627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:06 AM . Last Modified: ‎2024-03-19 01:09 AM

The SY32K48H-PD has space for 3 16KW power modules. This particular model comes with 2 modules installed for a total load of 32KW. You can add the additional module in the future for a total of 48KW. The UPS also has 3 rows of batteries internal (1 additional SYBT9-B4 can be ordered) but since you specified 1 hour of runtime the configurator included the additional battery frame SYCFXR48-9 which includes and additional 9 battery rows.



The vendor who recommended SY16K48H-PD with 3 x SYBT9-B4 did not look at your requirements. This only model can only support 16kw of load as sold and would not provide your 1 hour of runtime with the 3 SYBT9-B4 which is a row of batteries. In order to get a SY16K48H-PD to support your needs you would also have to purchase an additional power module SYPM10K16H and a populated XR battery frame SYCFXR48-9


http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SY32K48H-PD
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SYCFXR48-9

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:06 AM . Last Modified: ‎2024-03-19 01:09 AM

0 Likes
0
627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:06 AM . Last Modified: ‎2024-03-19 01:09 AM

Thanks Upsguy for your answers.

So, if I get the additional battery frame SYCFXR48-9, I will need 2 x rack cabinet space for the whole UPS. Is this correct?

The vendor also included the following. What does it do? Is this mandatory?
PDM1332IEC-3P
APC IT Power Distribution Module 3x1 Pole 3 Wire 32A 3xIEC309 300cm, 360cm, 420cm

Lastly, do I need a bypass switch?
Does the UPS come with one already?
This will allow the servers to continue to run on mains while maintenance is done on the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:06 AM . Last Modified: ‎2024-03-19 01:09 AM

0 Likes
0
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:06 AM . Last Modified: ‎2024-03-19 01:09 AM

Yes the UPS and Additional XR battery frame will take up the space of two server racks.

The UPS you are looking at has built in distribution that requires the prefabricated breaker and cordset module. This module clips into place inside the UPS to allow easily configurable distribution. The one you have been quoted has 3 whips each is a 3 Wire 32A IEC309 and the lenghts are 300cm, 360cm, 420cm.

I believe the UPS you are looking into can support up to 6 of these distribution modules. However you still have to stay within your load levels as you can add to many modules and load which would result in overloading the UPS.

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=PDM1332IEC-3P

As far as a Maintenance Bypass system. I think this should always be included if your load cannot be shut down for maintenance activities. Most maintenance actions can be performed on the UPS with it online however there are certain conditions that would require you to either be able to place the system into maintenance bypass or shutdown the load. I'm not very familiar with your regions Bypass enclosures and if there are currently and wall mount options however the full size unit with additional distribution is the:

http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=PDRPPH2000-M

This will also take up an additional amount of rack space.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of