Posted: 2023-01-09 10:59 AM
Dear friends:
I've been tasked with logging into our rack UPS systems and figuring out when batteries need to be replaced, etc. I have one unit that doesn't allow HTTP or HTTPS access, and when logging into the UPS via SSL I find that I'm an administrator (with the credentials that I have). and that there is a checksum error on the web server. I'm assuming this can get fixed at some point with a firmware upgrade. I'm trying to get at the detbat and detstatus commands, however, these show "command not found".
detbat -all
E101: Command Not Found
apc>
Wondering if this is also a result of the checksum problem.....or what this issue is?
Thanks for any help in advance. --- L
Schneider Electric Network Management Card AOS v6.6.4
(c) Copyright 2018 All Rights Reserved
-------------------------------------------------------------------------------
Name : apc030335 Date : 07/20/2022
Contact : Unknown Time : 22:14:13
Location : Unknown
User : Administrator
Up Time : 59 Days 23 Hours 1 Minute Stat : P+ N4+ N6+ A-
Type ? for command listing
Use tcpip command for IP address(-i), subnet(-s), and gateway(-g)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-10 03:59 PM
Hi @lkeyes
Schneider Electric Network Management Card AOS v6.6.4
(c) Copyright 2018 All Rights Reserved
-------------------------------------------------------------------------------
Name : apc030335 Date : 07/20/2022
Contact : Unknown Time : 22:14:13
Location : UnknownUser : Administrator
Up Time : 59 Days 23 Hours 1 Minute Stat : P+ N4+ N6+ A-
Based on the information above, we can see that the Application (A-) was not loaded correctly and this is the reason why the detstatus and detbat commands wouldn't work.
Kindly reflash the firmware by downloading it from the link below. I have shared FAQ articles below for your perusal.
Link copied. Please paste this link to share this article on your social media post.