Network management card reporting Warmstart every 2 minutes

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Network management card reporting Warmstart every 2 minutes
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:50 PM . Last Modified: β€Ž2024-03-07 02:22 AM

0 Likes
10
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:50 PM . Last Modified: β€Ž2024-03-07 02:22 AM

Network management card reporting Warmstart every 2 minutes

Hi all,

We have a SmartUPS-DP 10000 with a network management card I can administer through a web browser.

Last week I started recieving emails from the management card:
v1
Name : APC Smart-UPS DP 10000 XL
Location : Server Room
Contact : Rob Tyler
http://10.216.8.25

Serial # : JA0204000971
UPS Ser #: NA
Date: 12/07/2009
Time: 08:48:41
Code: 0x0002

Severe - System: Warmstart.

I get these emails every 2 minutes. I've tried resetting the management card by pressing the reset button on the back of the card, but the emails keep coming. Looks to me that the card is restarting itself every 2 minutes - does anyone know why it might be doing this, or what can be done to resolve it?

Thanks


Rob.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • apc
  • firmware
  • management
  • network_management_card
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:21 AM

0 Likes
0
3081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:21 AM

We are glad that it corrected the issue. Please let us know if you have any question in the future. Have a nice day πŸ™‚

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:50 PM . Last Modified: β€Ž2024-03-07 02:22 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:50 PM . Last Modified: β€Ž2024-03-07 02:22 AM

Hi all,

We have a SmartUPS-DP 10000 with a network management card I can administer through a web browser.

Last week I started recieving emails from the management card:
v1
Name : APC Smart-UPS DP 10000 XL
Location : Server Room
Contact : Rob Tyler
http://10.216.8.25

Serial # : JA0204000971
UPS Ser #: NA
Date: 12/07/2009
Time: 08:48:41
Code: 0x0002

Severe - System: Warmstart.

I get these emails every 2 minutes. I've tried resetting the management card by pressing the reset button on the back of the card, but the emails keep coming. Looks to me that the card is restarting itself every 2 minutes - does anyone know why it might be doing this, or what can be done to resolve it?

Thanks


Rob.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

Rob,

If you have any questions, please get back to us with the following details to provide you assistance.

Could you please let us know the exact Model and Serial number of the UPS and NMC as well? You can find these details on a white bar code sticker at the rear of the units. What is the firmware version of the NMC? Could you please post the event logs of the NMC?

Message was edited by: Techie

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

Good day Rob,

Please feel free to read this APC Knowledge Base article, this would give you an idea what causes a Coldstart and Warmstart events on a network management card. Please click --> here

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

JonPro - thanks for the article - I gave it a read and checked the network settings were OK and they do seem to be. Besides, nothing has changed on the UPS for months

Techie - I have found out the following information:

Model: Smart-UPS DP 10000 XL
Firmware Revision: 311.5.I
Manufacture date: 11/01/01
Serial Number: GS0144362959

I couldn't see a serial number on the network management card, only this:
"APC Smart Slot AP9617 Network Management Card"

How would I find out the firmware of the NMC?

Thanks


Rob.


Also, some sample logs:
12/07/2009 15:39:56 System: Web user 'apc' logged in from 10.216.28.35.
12/07/2009 15:39:11 System: Email: Could not resolve 'hrgex01.company.com'.
12/07/2009 15:38:49 UPS: Communications established.
12/07/2009 15:38:41 System: Warmstart.
12/07/2009 15:37:06 System: Email: Could not resolve 'hrgex01.company.com'.
12/07/2009 15:36:44 UPS: Communications established.
12/07/2009 15:36:36 System: Warmstart.
12/07/2009 15:35:00 System: Email: Could not resolve 'hrgex01.company.com'.
12/07/2009 15:34:38 UPS: Communications established.
12/07/2009 15:34:31 System: Warmstart.

HRGEX01 is our Exchange server. I have checked the DNS settings on the UPS and they are correct. I can do an nslookup of "hrgex01.company.com" using the same DNS server and get resolution OK, also if it can't resolve my mail server then how is it sending the emails to me?!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

Rob,

Can you send a screenshot of how does your network management card interface looks like? Based from what you gave us the serial number of your card is JA0204000971 and the part number is AP9617. If you can see tabs on the interface please click on Administration and then choose General and then click on About. If you can see menus on the left side then you need to click on Help and then About System.

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

Rob,

You can find the NMC firmware under Help/About System in the web interface or Administration-->General-->About.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:22 AM

OK guys,

NMC model number is AP9617
NMC serial number is JA0204000971
Hardware revision is 9

Application Module:
Name: sumx
Version 1.0.2

AOS information:
Version 1.0.2

Hope that helps

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:21 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:21 AM

Rob,

Please upgrade the NMC firmware version to the latest firmware and check if it corrects the situation. Click here to know the procedures to upgrade the NMC firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:21 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:21 AM

its most likely warmstarting due to the email failure. you also might want to reset the card to defaults (after backing up your config.ini file), and then seeing if you still have the same issue.

techie and jonpro can help you on how to backup the config.ini file if you need to.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:21 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:51 PM . Last Modified: β€Ž2024-03-07 02:21 AM

We are glad that it corrected the issue. Please let us know if you have any question in the future. Have a nice day πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore