Network card for SMT2200IC
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-2003:06 AM. Last Modified: 2024-11-2003:08 AM
If this is for an enterprise business you may purchase the AP9640, AP9641 NMC. Which has active development, technical support, and firmware updates.
This NMC has three branches of firmware that can be used. The old (AP9630/31) v7.XX firmware which is free and only sees security patches.
v2.XX firmware that is free but only receives limited development but security patches. v3.XX (SNS) which requires a paid subscription which has active development, technical support, and security patches.
If you’re a private user you may consider buying a used AP9630, AP9631 NMC which is EOL.
Development and technical support is EOL except for security related issues. The current firmware for the AP9630 / AP9631 is v7.1.8 firmware branch released this November 2024.
Questions Ask - If not please consider marking this reply as a solution if it answered your question. 👍