Need (updated) info on AP9537

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Need (updated) info on AP9537
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Buran
Crewman Buran
Crewman

Posted: ‎2022-08-10 12:46 PM . Last Modified: ‎2022-08-15 02:53 PM

0 Likes
4
4886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-10 12:46 PM . Last Modified: ‎2022-08-15 02:53 PM

Need (updated) info on AP9537

Hi everyone,

 

First, a (hopefully) easy question:

 

My AP9537 network card has been previously working with Office365  SMTP.  I need to reconfigure it to use SendGrid, but I keep getting "Bad user name or password".   The auto-generated passwords for SendGrid are 70 characters long (can't make them shorter), and now I'm wondering what the max password length is for the network card software.

 

(Update 8/15/22) - According to APC, the maximum password length is 256 characters, so password length isn't an issue.

 

 

Second, can anyone point me to the correct firmware updates for this thing?  After searching the site for a couple hours, I hit this:

UPS Network Management Card v7.0.4 Firmware for Smart-UPS & Galaxy 3500 with AP9630/31/35 - SFSUMX70...

 

But when I try to run it, I'm told the firmware isn't compatible.  

 

 

Thanks!

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Matt-B
Lieutenant JG Matt-B Lieutenant JG
Lieutenant JG

Posted: ‎2022-09-01 09:15 AM

In response to Buran
0 Likes
0
4750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-01 09:15 AM

Hi @Buran,

 

The "application module" is the firmware type that you would need to run in your system - in this case, SUMX, which is used for our second generation Network Management Card (NMC2) in a SmartUPS. The latest version of SUMX we have is v7.0.8, which can be downloaded here: https://www.apc.com/us/en/product/SFSUMX708/ups-network-management-card-v7-0-8-firmware-for-smartups...

 

If you're having issues upgrading the firmware, you can try to do it manually over FTP instead of using the bundled firmware upgrade wizard - we have instructions on how to do that here: https://www.apc.com/us/en/faqs/FA156047/#FTP

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-08-26 07:41 AM

0 Likes
2
4793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-26 07:41 AM

Hi @Buran 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.

 

To assist you with your query, it would be helpful if you can provide the actual hardware that you have where the AP9537 is installed to.  I am guessing that this is installed on an APC Rack PDU 2nd Generation.  

 

If this is the case, the firmware that you have posted is meant to be used for network management cards (NMC) that are installed on a UPS.

 

You may download the latest rPDU firmware from this link, APC Rack Power Distribution Unit Firmware, Revision 7.0.8, For AP8xxx and AP7xxxB Series PDUs.

 

Should you need some help in upgrading the firmware, you may refer to this article, How do I upgrade the firmware on an APC Network Management Card (NMC) or NMC embedded device (Rack P... 

 

I hope this helps.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Buran
Crewman Buran
Crewman

Posted: ‎2022-09-01 06:58 AM

In response to JonPro
0 Likes
1
4757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-01 06:58 AM

Hi @JonPro 

 

I hope this is the info you need:

 

UPS
-------

Model
Smart-UPS SRT 5000
SKU
SRT5KRMXLT

 

Network Card
-------------------
Model Number
AP9537SUM
Serial Number
5A1838T00040
Hardware Revision
05
Manufacture Date
09/21/2018


Application Module
Name
sumx
Version
v6.5.6
Date
Apr 6 2018
Time
16:00:53

 

APC OS (AOS)
Name
aos
Version
v6.5.6
Date
Mar 30 2018
Time
16:51:08

 

APC Boot Monitor
Name
bootmon
Version
v1.0.8
Date
Apr 8 2014
Time
10:59:40

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Matt-B
Lieutenant JG Matt-B Lieutenant JG
Lieutenant JG

Posted: ‎2022-09-01 09:15 AM

In response to Buran
0 Likes
0
4751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-01 09:15 AM

Hi @Buran,

 

The "application module" is the firmware type that you would need to run in your system - in this case, SUMX, which is used for our second generation Network Management Card (NMC2) in a SmartUPS. The latest version of SUMX we have is v7.0.8, which can be downloaded here: https://www.apc.com/us/en/product/SFSUMX708/ups-network-management-card-v7-0-8-firmware-for-smartups...

 

If you're having issues upgrading the firmware, you can try to do it manually over FTP instead of using the bundled firmware upgrade wizard - we have instructions on how to do that here: https://www.apc.com/us/en/faqs/FA156047/#FTP

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Buran
Crewman Buran
Crewman

Posted: ‎2022-12-19 03:01 PM

0 Likes
0
4589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-19 03:01 PM

Thanks Matt.   I held off on doing this for a while, but everything updated with no problems.  Thanks for pointing me in the right direction.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore