Ask our Experts
Didn't find what you are looking for? Ask our experts!
Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-30 04:52 AM . Last Modified: 2024-03-08 03:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:52 AM . Last Modified: 2024-03-08 03:58 AM
We have a Smart-UPS 3000 RM (Model: SU3000R3IBX180) that is seemingly calculating the battery runtime incorrectly.
The calculated runtime at 41% load and 100% battery charge stays somewhere between 60 and 120 secs.
Since the estimated runtime is not more that 2 mins, the UPS is permanently in a 'Low Battery' state (with the front-panel LEDs flashing),
and the monitoring software therefore forces an immediate shutdown any time there is a wobble in our mains supply and the UPS goes
onto battery, even if it's only for a few seconds.
The replace battery light came on a couple of weeks ago, although it went off again a few days later; I have just replaced the batteries
(which were a little over a year old) with brand new ones, but it has made no difference. I tried a self-test and and completely powered the
unit off and disconnected from the mains to try to force it to recalculate the runtime, but without any luck.
So I need the battery constant for manual battery reset ( [http://www.rm.com/Support/TechnicalArticle.asp?cref=TEC817072] )
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:52 AM . Last Modified: 2024-03-08 03:58 AM
i will private message you the battery constant value.
APC cannot be liable for any damage caused to the UPS during this procedure if you are not familiar with the tools that the procedure uses.
I'd recommend writing down the current value that the UPS is at so if something goes wrong, you can at least put it back to that value.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:52 AM . Last Modified: 2024-03-08 03:58 AM
i will private message you the battery constant value.
APC cannot be liable for any damage caused to the UPS during this procedure if you are not familiar with the tools that the procedure uses.
I'd recommend writing down the current value that the UPS is at so if something goes wrong, you can at least put it back to that value.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.