Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Need help with AP7932

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Need help with AP7932
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:04 AM . Last Modified: ‎2024-03-18 12:54 AM

0 Likes
5
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:04 AM . Last Modified: ‎2024-03-18 12:54 AM

Need help with AP7932

Hello,

I have rack PDUs that are AP7932's and I want to remotely manage and monitor them, but I'm having trouble. How do you remotely manage these? Through web interface? SSHing? I've tried those ways and nothing works. Perhaps I'm configuring them wrong? I am able to ping the IPs that I'm using. If anyone could help me out I would really appreciate it.

Thanks,

Andrew

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap7932
  • manage
  • network
  • remotely
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

wink Glad you're all set.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:04 AM . Last Modified: ‎2024-03-18 12:54 AM

0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:04 AM . Last Modified: ‎2024-03-18 12:54 AM

Hi Andrew,

These offer HTTP (default), HTTPS (configurable), Telnet (default), SSH (configurable), SNMPv1/v3, FTP, and SCP (when SSH is configured) for access.

How did you configure an IP on the device? I would verify that you followed the instructions, at least one method, we have outlined here for NMC1 (which is what this device falls under)-> How do you make a Network Management Card communicate on a network? | FAQs | Schneider Electric US

If you followed those instructions and you can verify the settings stuck (because they do require you to log out or reboot the PDU for them to take effect), perhaps at least by verifying the IP on the PDU by holding down the "control" button that is to the right or bottom of the 7-segment display for five seconds and it will say "IP" and scroll the IP across the screen (see below for diagram), then I'd check to make sure you don't have a proxy server configured that cannot access the PDUs, verify you have a solid green status LED on the PDU itself (LED that has a checkmark or X next to it on the network jack) and verify you have a link LED on the network jack (LED that says 10/100).

Here is the "control" button - again, hold it down for 5 seconds or so until it says "IP" and let go and it will scroll the IP address across the screen.

1415_pdu.jpg

Hope that helps get you started.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:54 AM

0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:54 AM

I figured it out. I didn't realized there was a proxy server/fire wall that I had to go through lol. Thank you for the help

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:54 AM

0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:54 AM

Hi Angela,

Thanks for responding. I have configured the PDU by directly connecting to the serial port and have done exactly as it says below

  • Apply the port settings to establish the connection.
  • Press 3-5 times to display the username prompt.*
  • Use the default username and password of  "apc"

You are now in the control console.

  • Choose "Network"
  • Choose "TCP/IP"
  • Choose "Boot mode"
  • Change Boot mode to "Manual"
  • Set the system IP, subnet mask, and default gateway.
  • Accept changes.
  • Press Ctrl-C to return to main menu.
  • Log out of console to save changes.

To confirm that the settings stuck I have held down the button and the correct IP shows. I have also pinged the IP in a terminal window and the IP is able to be pinged once I configured the PDU. However, I can't access the web interface when I put in the IP. It just does not load anything. I'm quite confused

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:54 AM

0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:54 AM

What about the link LED (which I assume is fine assuming you haven't made a typo on the IP you're accessing) or proxy server I mentioned? Is it possible there is a typo in the subnet mask?

You could also try a direct connection to the PDU (with a crossover cable if you don't have 1000mbps enabled NIC) and see if you can access it that way (if that's not already what you're doing).

Lastly, were these brand new or previously configured? If you're not sure or they were used, you could also try resetting the unit to defaults (you can either include or exclude TCP/IP settings in that command) which is available under Main Menu->System->Tools I believe.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

0 Likes
0
1077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

wink Glad you're all set.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of