Need help configuring my nmc and powerchute network edition

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Need help configuring my nmc and powerchute network edition
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:13 AM . Last Modified: ‎2024-03-11 04:14 AM

0 Likes
4
1227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:13 AM . Last Modified: ‎2024-03-11 04:14 AM

Need help configuring my nmc and powerchute network edition

Hi there. My first post here.

I have a simple configuration based on an apc smart ups 1500Va with a nmc (Ip already configured) and two physical hosts (esxi ) connected to ups. What I'd like to achieve is very simple. My ups has a 25 minutes runtime with this load ( two hosts plus network switch) . I'd like to gracefully shutdown the vms in case of a power outage. At the moment I've installed powerchute network edition on a vm just for testing purpose . nmc sees correctly the machine's ip but I don't know ho to set all the parameters. here is waht I'd like to achieve:

the ups goes on battery---->After 600 seconds it sends a shutdown signal to all the vms (aprox. time in order to complete the poweroff sequence: 180 seconds). The ups then shuts down itself and restart when the power is back. Would you be so kind to to tell me what to set on the nmc and what on the agent ? 

thanks in advance.

Max

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:14 AM . Last Modified: ‎2024-03-11 04:14 AM

0 Likes
0
1227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:14 AM . Last Modified: ‎2024-03-11 04:14 AM

Sorry for this misunderstanding. Actually I can install PCNS on each of my vms without any issue . I have a total of 15 vm's but just two must stay powered on until the ups shuts down as they are presenting the storage to the esxi. In other words, they will crash when battery power will be cut off. But I need to gracefully shut down the other 13 vm's . My smart ups has aprox. 25 minutes of runtime available. How do I set the NMC shutdown page if I want to shutdown my vms after, let's say, 10 minutes and considering that they need 150 sec. tu completely turn off ?

thanks again.best regards

Max

Italy

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:13 AM . Last Modified: ‎2024-03-11 04:14 AM

0 Likes
0
1227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:13 AM . Last Modified: ‎2024-03-11 04:14 AM

Hi,

The basic setup is, install PowerChute Appliance on each host. The Appliance tell the host when it should shut down and the host then tells the VMs to power down. See http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/84099/vm-pr... for information on powering down the VMs. 

To get the host to start automatically you need to configure PowerChute to tell the UPS to turn off. This is available in the PowerChute web interface under shutdown settings. In the BIOS of the host server you need to set it to power on when AC is restored. The UPS will power down once the hosts have powered down. Then when AC is restored the UPS will power back up and the hosts will power up when the UPS begins to provide AC. You will need to configure either low battery threshold on shutdown delay for outlet group/s depending on the UPS type and model to be sure that AC is not cut to the host prior to them shutting down completely. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:14 AM . Last Modified: ‎2024-03-11 04:14 AM

0 Likes
0
1227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:14 AM . Last Modified: ‎2024-03-11 04:14 AM

thanks Bill for your reply but I cannot use the virtual appliance and here is the reason why:

the local storage of both hosts has been virtualized through a software called datacore vsan and it is managed by two virtual appliance which are exposing the storage to the esxi via iscsi . these vms should never be powered off or better but I don't think I can exclude them from the shutdown process. That's the reason why I'd go with the installation of powerchute network edition on each vm.

Related to the nmc, here is the screenshot that I find under configuration--->shutdown

(the nmc has been configured by a tech guy and not by myself) What's the meaning of the values?

how does the ups work based on this configuration?

f3Ii48qldEeTgD0GZOyTgw%3D%3D.pngf3Ii48qldEeTgD0GZOyTgw%3D%3D.png

and here is the screenshot from an agent installed on a vm. Which line shall I configure and how ?

thanks again

Max

XhBnMO4e8bYpxJOln62DWw%3D%3D.pngXhBnMO4e8bYpxJOln62DWw%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:14 AM . Last Modified: ‎2024-03-11 04:14 AM

0 Likes
0
1227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:14 AM . Last Modified: ‎2024-03-11 04:14 AM

Hi,

What you are doing is not a supported configuration. If you cannot install PCNS on a VMware vMA or install the Appliance your option is to install PCNS on a Windows system that is out side of the host (physical computer). Then configure PCNS on the Windows system to communicate with the host to power down. 

the settings for the NMC and PCNS are all described in the help files and the PCNS events are also listed in the User's Guide starting on page 101. 

Examples:

Low Battery Duration
A runtime remaining threshold, below which a low battery condition is triggered on the UPS. For example, if the Low Battery Duration is set to ten minutes, and the UPS predicted runtime remaining reaches ten minutes or below, a low battery condition is triggered. If input power is not restored to the UPS, it will turn off when the battery has exhausted.
The runtime remaining has dropped below the configured threshold while on Battery.

The runtime remaining has dropped below the configured threshold while on battery. You can configure this threshold using the shutdown action on the Configure Events page.

When the UPS in running on battery power and the runtime remaining on the UPS drops below the threshold, PowerChute will trigger a shutdown sequence. See “Sequenced Server Shutdown” for more information.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:14 AM . Last Modified: ‎2024-03-11 04:14 AM

0 Likes
0
1228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:14 AM . Last Modified: ‎2024-03-11 04:14 AM

Sorry for this misunderstanding. Actually I can install PCNS on each of my vms without any issue . I have a total of 15 vm's but just two must stay powered on until the ups shuts down as they are presenting the storage to the esxi. In other words, they will crash when battery power will be cut off. But I need to gracefully shut down the other 13 vm's . My smart ups has aprox. 25 minutes of runtime available. How do I set the NMC shutdown page if I want to shutdown my vms after, let's say, 10 minutes and considering that they need 150 sec. tu completely turn off ?

thanks again.best regards

Max

Italy

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore