Near continual Self Tests on new Smart-UPS 3000 RM XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Near continual Self Tests on new Smart-UPS 3000 RM XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:37 AM

0 Likes
2
674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:37 AM

Near continual Self Tests on new Smart-UPS 3000 RM XL

We replaced a dead (malfunctioning) UPS yesterday with a Smart-UPS 3000 RM XL, and started apcupsd to monitor it about 7PM yesterday (It was powered up in the morning). Currently there is no load on the UPS. Today apcupsd started reporting near continual Self Tests.

I just tried APC's chat line, but they're not in the office today.

I was hoping someone here might be able to give suggestions as to what is happening.

I'm hoping there's a way to recover from this and that the UPS is not DOA.


Status at first test this morning:

Dec 24 10:38:20 U06FACVS apcupsd[19966]: 118.8,118.8,118.8,54.54,60.00,00.0,15.3,000.0,000.0,118.8,100.0,0
Dec 24 10:38:31 U06FACVS apcupsd[19966]: UPS Self Test switch to battery.
Dec 24 10:38:31 U06FACVS apcupsd[19966]: 118.8,118.8,120.1,53.46,60.00,00.0,15.3,000.0,000.0,118.8,100.0,1
Dec 24 10:38:37 U06FACVS apcupsd[19966]: UPS Self Test completed: Battery OK
...
Dec 24 11:55:02 U06FACVS apcupsd[31023]: 118.8,118.8,120.1,49.95,60.00,00.0,15.7,000.0,000.0,118.8,066.0,1
Dec 24 11:55:08 U06FACVS apcupsd[31023]: Mains returned. No longer on UPS batteries.
Dec 24 11:55:08 U06FACVS apcupsd[31023]: Power is back. UPS running on mains.
Dec 24 11:55:21 U06FACVS apcupsd[31023]: UPS Self Test switch to battery.
Dec 24 11:55:21 U06FACVS apcupsd[31023]: 118.8,118.8,120.1,50.22,60.00,00.0,15.7,000.0,000.0,118.8,066.0,0
Dec 24 11:55:32 U06FACVS apcupsd[31023]: 118.8,118.8,120.1,49.95,60.00,00.0,15.7,000.0,000.0,118.8,065.0,1
Dec 24 11:55:42 U06FACVS apcupsd[31023]: 118.8,118.8,120.1,49.95,60.00,00.0,15.7,000.0,000.0,118.8,065.0,0
Dec 24 11:55:52 U06FACVS apcupsd[31023]: 118.8,118.8,120.1,49.95,60.00,00.0,15.7,000.0,000.0,118.8,065.0,1
Dec 24 11:56:01 U06FACVS apcupsd[31023]: Running on UPS batteries.
Dec 24 11:56:03 U06FACVS apcupsd[31023]: 118.8,118.8,120.1,49.95,60.00,00.0,15.7,000.0,000.0,118.8,065.0,0
Currently:
APC : 001,053,1324
DATE : Fri Dec 24 12:06:45 PST 2010
HOSTNAME : U06FACVS
RELEASE : 3.14.2
VERSION : 3.14.2 (15 September 2007) debian
UPSNAME : ups06
CABLE : Custom Cable Smart
MODEL : Smart-UPS 3000 RM XL
UPSMODE : Stand Alone
STARTTIME: Fri Dec 24 11:19:05 PST 2010
STATUS : ONBATT
LINEV : 118.8 Volts
LOADPCT : 0.0 Percent Load Capacity
BCHARGE : 062.0 Percent
TIMELEFT : 176.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
MAXLINEV : 118.8 Volts
MINLINEV : 118.8 Volts
OUTPUTV : 120.1 Volts
SENSE : High
DWAKE : 000 Seconds
DSHUTD : 090 Seconds
DLOWBATT : 02 Minutes
LOTRANS : 106.0 Volts
HITRANS : 127.0 Volts
RETPCT : 000.0 Percent
ITEMP : 15.7 C Internal
ALARMDEL : 5 seconds
BATTV : 50.0 Volts
LINEFREQ : 60.0 Hz
LASTXFER : Automatic or explicit self test
NUMXFERS : 25
XONBATT : Fri Dec 24 11:55:21 PST 2010
TONBATT : 685 seconds
CUMONBATT: 2454 seconds
XOFFBATT : Fri Dec 24 11:55:08 PST 2010
LASTSTEST: Fri Dec 24 11:49:31 PST 2010
SELFTEST : NO
STESTI : 336
STATFLAG : 0x07060010 Status Flag
REG1 : 0x00 Register 1
REG2 : 0x00 Register 2
REG3 : 0x00 Register 3
MANDATE : 09/18/10
SERIALNO : JS10380xxxx
BATTDATE : 09/18/10
NOMOUTV : 120
NOMBATTV : 48.0
EXTBATTS : 0
FIRMWARE : 691.19.D
APCMODEL : FWD
END APC : Fri Dec 24 12:06:46 PST 2010

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 940-0024e
  • apc
  • self_test
  • smart-ups
  • smart_cable
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:37 AM

0 Likes
0
674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:37 AM

yes, i agree. it was probably an older, faulty serial cable. we have seen this before.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:37 AM

0 Likes
0
674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:37 AM

This apparently turned out to be a serial cable problem. We continued to use the previous cable (940-1524C) rather than the one that came with the new UPS (940-0024E).

Apparently the wrong cable worked ok initially. It seems like it behaved differently when the UPS decided to do a Self Test.

Some of the symptoms:

1. When I got to the UPS, it was on the battery. The online light was off. After a while, the online light would come back on and blink about 20 times before turning off again.

2. When I tried to turn off the UPS by holding in the power button, it would start back up when I released the button.

When I unplugged the 940-1524C cable, the UPS showed the online light and was no longer on the battery. When I plugged in the 940-0024E cable, everything seemed to work. Of course, there could still be another problem that shows up the next time it does a Self Test.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:37 AM

0 Likes
0
675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:37 AM

yes, i agree. it was probably an older, faulty serial cable. we have seen this before.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of