Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

NMC2 on SmartUPS2200 SNMPv3 "Unauthorized User"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: NMC2 on SmartUPS2200 SNMPv3 "Unauthorized User"
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
mdjezierski_apc
Crewman mdjezierski_apc
Crewman

Posted: ‎2021-07-08 01:56 AM

0 Likes
6
587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:56 AM

NMC2 on SmartUPS2200 SNMPv3 "Unauthorized User"

This was originally posted on APC forums on 4/4/2017


Hello APC -

I am having the same issue with a SmartUPS2200SMT with a NMC2 that Adam recently had in his post about a similar issue. However, I am on the latest AOS 6.4.6, sumx 6.4.6 and APC Boot monitor 1.0.8

I use Zabbix as the NMS, and I have 10 other APC devices ranging from SmartUPS 3000 to 8000 with NMC2 on this same AOS, and multiple APC PDU's running the latest firmware without any issues. On the NMC2 with the "unauthorized user" issue, the IP address in the authorized section IS the IP address of Zabbix. In the logs I see multiple lines of "Detected an unauthorized user attempting to access the SNMPv3 interface from w.x.y.z" where w.x.y.z is the IP address of Zabbix. The Zabbix server is single homed, only one IP address assigned to it.

SNMPv1 is DISABLED.

My troubleshooting steps to date:

1. Reset all parameters of the NMC2 to factory default

2. Remove the entry for the SU2200 in Zabbix, clone entry from known working APC device entry and change the target IP to that of the SU2200 NMC

3. Change the SNMPv3 IP range allowed on NMC to 0.0.0.0

4. Used the config.ini to reset the username, authorization password and privacy password, verified in Zabbix and the APC both are using MD5 and DES, which works on all our other APC devices

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mdjezierski_apc
Crewman mdjezierski_apc
Crewman

Posted: ‎2021-07-08 01:57 AM

0 Likes
0
585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:57 AM

This was originally posted on APC forums on 4/17/2017


We performed a background OS update on the Zabbix server and rebooted the NMS. We no longer have the issue with the "unauthorized user" on the NMC2, and we are receiving data in Zabbix.

See Answer In Context

Reply
Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:56 AM

0 Likes
0
585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:56 AM

This reply was originally posted by Angela on APC forums on 4/5/2017


Hi Michael,

Let me check into this. We recently added support in v6.4.6 for the NMC to be able to report unauthorized attempts for SNMPv3 interface - previously it was only supported for unauthorized v1 attempts. After this was added, I have seen a few issues with SNMPv3 now.

I think you've done all of the proper troubleshooting on it.

Would you be able to get a packet capture of this happening - where? I would like to ask someone else about it and I think they may ask for the packet capture. Let me know if it is feasible.

Also, is Zabbix able to report data successfully from the NMC even with these errors in the log?

Lastly, I will be on vacation until next Tuesday after today but I will try to keep up with this if you can respond back about packet capture. If you're able to get it, I can give you a special email address to send it to so you don't have to post it publicly here.

Reply
mdjezierski_apc
Crewman mdjezierski_apc
Crewman

Posted: ‎2021-07-08 01:56 AM

0 Likes
0
585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:56 AM

This was originally posted on APC forums on 4/5/2017


I'll set up to do a packet capture this afternoon. If you would pass along that email address I'll send the captures along.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:56 AM

0 Likes
0
585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:56 AM

This reply was originally posted by Angela on APC forums on 4/5/2017


OK, thanks. Just let me know what IPs are what and if you have feedback on those other questions. You can include that info in a .txt file that you can also send to the address or here on the forum. SNMPv3_.rg147cvnpf63919e@u.box.com is the email address.. it will go to a Schneider Electric Box folder I've set up.

If the files are too big to go over email, I'll send you an alternative method to upload to this folder via private message.

Reply
mdjezierski_apc
Crewman mdjezierski_apc
Crewman

Posted: ‎2021-07-08 01:56 AM

0 Likes
0
585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:56 AM

This was originally posted on APC forums on 4/5/2017


I have a packet capture and through additional troubleshooting, I found that unless I turn off MD5/DES or SHA/AES authentication and privacy, I get the "unauthorized user" message. I still have SNMPv3 running and it has a username in place, and I am pulling SNMPv3 data.

Answering the previous question, when I get the "unauthorized user" errors, no SNMP data is passing from the APC and Zabbix NMS.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:56 AM

0 Likes
0
585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:56 AM

This reply was originally posted by Angela on APC forums on 4/5/2017


My gut tells me you're experiencing this issue (or another symptom of it): http://www.apc.com/us/en/faqs/FA305661 but instead of seeing it with our SNMP NMS (Data Center Expert), you're seeing it with Zabbix.

With our NMS, we reboot it and the issue goes away but I am not familiar enough with Zabbix to know what the equivalent process would be to reset the SNMPv3 communication parameters and to let communication continue with auth and privacy. I am not aware of anyone else who has seen the issue on something other than Data Center Expert yet, though I figured it was possible.

This issue was caused by a bug in AOS 6.4.6 SNMPv3 discovery so depending on what you're able to do or try, rebooting or resetting Zabbix in some form may fix it. You'd also want to do it after all of your devices have been upgraded to AOS 6.4.6. Another option is that we could try to downgrade the NMC to the previous firmware rev which would fix this also. I don't like suggesting this but it may be easier depending on if you can figure out how to "reboot" Zabbix or reset to allow SNMPv3 communication to be successful again. 

Within our software, even removing and re-adding the device does not work to solve the issue if the device is re-added with the same ID. (I didn't do enough personal testing so I am not 100% sure what ID the SNMPv3 agent ID is identified by in our system or also in Zabbix - IP or maybe SNMPv3 engine ID. I thought maybe if one of those things was changed, deleting and re-adding would work. In Zabbix, not sure if trying this is possible and/or if that means you lose historical data but I imagine so like in our tool.)

Reply
mdjezierski_apc
Crewman mdjezierski_apc
Crewman

Posted: ‎2021-07-08 01:57 AM

0 Likes
0
586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:57 AM

This was originally posted on APC forums on 4/17/2017


We performed a background OS update on the Zabbix server and rebooted the NMS. We no longer have the issue with the "unauthorized user" on the NMC2, and we are receiving data in Zabbix.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc