NMC2 does not detect UIO probes if UPS is not responding

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC2 does not detect UIO probes if UPS is not responding
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:05 PM

0 Likes
10
3760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:05 PM

NMC2 does not detect UIO probes if UPS is not responding

[Unrelated to my other question about Symmetra RM unexpected shutdowns, I just found it in my queue and remembered to post it.]

The AP9631 will not detect / report on any attached UIO probes until it can successfully communicate with the attached UPS (sumx or sy, depending on the firmware loaded on the NMC2).

This is a rather odd condition, so let me explain... I use either an AP9617 with an AP9312 module and AP9312TH sensors in a triple expansion chassis and power supply, or an AP9619 with an AP9312TH sensor in a single-slot chassis with power supply as a stand-alone environmental monitoring system. I had started with AP9319's, but those were orphaned a week after I bought them (the AP9319 is so orphaned that it doesn't even show up if you search the APC site for it). So I built my own, long before NetBotz. The only cosmetic issue is that the web page reports "Searching for a UPS", but SNMP monitoring / traps from the sensors works perfectly.

I decided to try using an AP9631 (firmware 6.2.1) with AP9335TH sensors, again in the single slot chassis (AP9600) with power adapter (AP9505). It does not detect the sensors. There is no listing for "Universal I/O" in the "Status" tab (nor is there one for "UPS", but that is expected).

I installed that same AP9631 and AP9335TH's in a Symmetra RM and the Universal I/O is detected, along with the UPS. I did not test to see what would happen if the NMC2 loses communication with the UPS - the Universal I/O may continue to work, I'm not sure. It appears that this is a regression from the older AP9617/8/9 cards, which did detect the sensors even when no UPS was present. 

The next time someone is working on the NMC2 firmware, would it be possible to check and see if this is easy to fix? I'd like to upgrade these to NMC2's for the improved security features, but I'm not willing to buy a UPS for each to make them happy sealed - these are at sites with multiple giant (500KW and larger) facility UPSs in place.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:05 PM

0 Likes
0
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:05 PM

Hi Terry,

Take a look here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156184 

You can probably get it working on v5.1.7 per that kbase but I did have a bug logged on this behavior for v6 firmware as it seems it never got ported over. I will see if they can squeeze it in for the next release since maybe they can port the fix from v5.1.7.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

Hi Terry, just to confirm, we will have it addressed in the next revisions of sumx and sy applications as the developer was able to squeeze it in. Now I just need to make sure it makes it to all apps that support UIO. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

That's wonderful, thanks for the lighning fast service!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

Hello  Angela 

I am experiencing the same issue here with an AP9631 running v6.5.6 AOS and sumx application v6.5.6. It is installed in an AP9600 chassis with no UPS connection. The NMC reports "There are no sensors connected" despite the presence of an AP9335T on the UIO port. Can you confirm that this issue was addressed and suggest next steps for troubleshooting?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

Hi Patrick,

I just spent a little time looking at this. We did fix this but I see as of 6.5.6, it appears to be broken in some way again. As late as v6.5.0 it works.

So, the best option I see is to use AOS/sumx v6.5.0 if you need this to work immediately. In the meantime, I will see if we can fix it for a future release. We have a 6.6.4 coming in a few weeks but I think it will be too late in the development process to fix it in that rev unfortunately but I'll see - just wanted to set expectations.

If you want to load 6.5.0 sumx, you can get it here: ftp://restrict:Kop$74!@ftp.apcc.com/restricted/hardware/nmcard/firmware/sy/650/apc_hw05_aos650_sy650... 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

Thank you for the fast and comprehensive response, Angela. I'll give version 6.5.0 a try and see how that goes. If you can update this thread when the fix is rolled into a future firmware update, that would be appreciated!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

Confirmed this is working in v6.5.0

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

On 7/30/2018 3:52 PM, Angela said:

We have a 6.6.4 coming in a few weeks but I think it will be too late in the development process to fix it in that rev unfortunately but I'll see - just wanted to set expectations.

It is still broken as of 6.7.2 (but not noted in the "known problems" section of the release notes). Can you bug someone to make sure it gets fixed in the next release? Also, it would be nice if a test for this got added to the QA testing - this regression has come back a couple of times after being fixed.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:43 AM . Last Modified: ‎2024-02-29 11:04 PM

Hi Terry,

I have added your comments to the engineering notes. The issue is listed to be address in a future release.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
3763
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.