Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
NMC2(AP9630) (AOS 7.0.4) Email send not working (TLS SMTP issue)
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-1402:17 PM
NMC2(AP9630) (AOS 7.0.4) Email send not working (TLS SMTP issue)
Have others found this issue?
An AP9630 on the latest AOS 7.0.4 cannot send emails to an SMTP server using TLS or StartTLS if the SMTP server's initial TLS negotiation is too big. My SMTP server's TLS 'Server Hello, Certificate and Server Hello Done' is 5645 bytes. The maximum size supported by the AP9630 is probably 4344 bytes, based on the TCP Window size seen in the TCP negotiation.
To spot the problem:
- The Email test fails
- A packet capture of the network traffic shows 'TCP ZeroWindow' packets from the NMC2 after the initial TLS 'Server Hello' packets from the SMTP server.
The only way of fixing this that I have found is to use another SMTP server with a smaller certificate chain.