NMC1 Cards AP9618 AP9619 Config Files and stubborn emails
Hi. I'm in the process of mass configuring about 100 x NMC cards (generally AP9618, AP9619 and some NMC2 cards) and only want 'genuine' fault messages to be emailed to me. I've pretty much achieved this but keep getting 'Self-test passed' emails sent to me (0x0105), even though I've masked it out in the config.ini file.
For example, the email message content is as follows:
Date: 10/10/2016
Time: 20:59:53
Code: 0x0105
Informational - UPS: passed via internal operation a self-test.
But the line in the config.ini file is as follows:
; UPS: Passed a self-test.
E0105=ES,E[:::],T[:::::],P[:::]
So, the settings within the 'E' brackets should mean that emails are masked to all recipients - yet the cards keeps sending them! Any ideas why and/or how we can prevent this? Also, I've noticed in some config files, there are '-' signs between the colons. What does this mean?
PS The firmware AOS Version is V3.7.3 & APP is V3.7.2
Many thanks.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2021-06-29 05:34 AM . Last Modified: 2024-03-13 12:52 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:34 AM . Last Modified: 2024-03-13 12:52 AM
Thanks Angela, this has resolved the issue.
Once I'd followed this procedure, I then read the config.ini file again and as I queried in my original post, inserting a '-' between the colons in the email recipient brackets masks the 'clearance' emails from being sent.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:34 AM . Last Modified: 2024-03-13 12:52 AM
Hi Richard,
Please read this knowledge base article as far as how to disable self test passed event along with the caveats: http://www.apc.com/us/en/faqs/FA156104
Please read this knowledge base on understanding the config.ini and its syntax even though we don't recommend editing it directly due to its complexity and nuances: http://www.apc.com/us/en/faqs/FA156188
Hope these cover your questions.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 05:34 AM . Last Modified: 2024-03-13 12:52 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:34 AM . Last Modified: 2024-03-13 12:52 AM
Thanks Angela, this has resolved the issue.
Once I'd followed this procedure, I then read the config.ini file again and as I queried in my original post, inserting a '-' between the colons in the email recipient brackets masks the 'clearance' emails from being sent.