APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-28 10:56 PM . Last Modified: 2024-03-14 03:53 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:56 PM . Last Modified: 2024-03-14 03:53 AM
When scheduling self-test selection: 7 Days, 14 Days. When does the actual test run? If I select 7 Day and apply the settings on Monday at 3:00 am will it run every Moday at 3:00 am. Can I set it to run at a different time, say Saturday at 12:02 PM?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:56 PM . Last Modified: 2024-03-14 03:53 AM
The NMC self test scheduling is as you said, none, 7 days, or 14 days. The self test will run 7 or 14 days after you have applied the setting to the NMC/UPS. There is no way to change that option.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:56 PM . Last Modified: 2024-03-14 03:53 AM
The NMC self test scheduling is as you said, none, 7 days, or 14 days. The self test will run 7 or 14 days after you have applied the setting to the NMC/UPS. There is no way to change that option.