Multiple UPS’s connected to one server for monitoring only?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Multiple UPS’s connected to one server for monitoring only?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:21 PM . Last Modified: ‎2024-03-06 03:17 AM

0 Likes
3
1050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:21 PM . Last Modified: ‎2024-03-06 03:17 AM

Multiple UPS’s connected to one server for monitoring only?

Hi,

New to forums and I wonder if anyone can help? for our comms racks we have four ups’s 2 x 1500’s and 2 x 1400’s, I’m unable to install or connect the UPS’s to the comms equipment so I have built a server that sit’s within one of the cabs and all four UPS’s connect to this machine (2 x serial, 2 x USB).

I have just purchased Powerchute Business Edition (5 Node version) thinking this would allow me to monitor the 4 UPS’s from this machine but in reality the 5 licenses allow me to monitor 5 servers, this is the obosite of what I need.
Any idea’s on how I can achieve what I require?

Cheers

Stu

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:21 PM . Last Modified: ‎2024-03-06 03:17 AM

0 Likes
0
1050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:21 PM . Last Modified: ‎2024-03-06 03:17 AM

hmm, ok well..there may not be a really cheap way to do this.

if you want to do monitoring via USB or serial, you'd need to have a server/OS running with PCBE attached to each UPS. this may be cheaper in the long run but not physically feasible.

more expensively but a cleaner solution would be installing a [APC Network Management Card|http://www.apc.com/products/family/index.cfm?id=98] in each UPS so you can monitor each UPS via the network remotely. based on what you need, i recommend looking at AP9630. on the one server you want to shutdown, you can install the free Powerchute Network Shutdown and when installing the software, provide it the network address of the Network Management Card in the UPS it is attached to for power so that when the UPS is running low on battery or based on a specific configuration you complete, the NMC will send a shutdown signal over the network that the PCNS software will pick up and initiate a graceful shutdown on the server. PCNS also must be compatible with the server you are running for this to work. here is the compatibility chart -> http://www.apcmedia.com/salestools/SJHN-7AYQNP_R21_EN.pdf

hope this helps. i cant think of any other way to do what you need to unfortunately.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:21 PM . Last Modified: ‎2024-03-06 03:17 AM

0 Likes
0
1050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:21 PM . Last Modified: ‎2024-03-06 03:17 AM

when you say monitor - do you mean for the server to look at all the UPSs and only shutdown when all four shutdown or do you want to just be able to monitor UPS status information from all four units at one time and you do not need a graceful shutdown? how many of the UPSs is the server connected to for power?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:21 PM . Last Modified: ‎2024-03-06 03:17 AM

0 Likes
0
1050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:21 PM . Last Modified: ‎2024-03-06 03:17 AM

thank you for the reply

I just monitor the ups status for all four devices, (Load, health etc etc) and then send an email if any issues are found. the server is connected to only one of the ups's for power.

Cheers
Stu

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:21 PM . Last Modified: ‎2024-03-06 03:17 AM

0 Likes
0
1051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:21 PM . Last Modified: ‎2024-03-06 03:17 AM

hmm, ok well..there may not be a really cheap way to do this.

if you want to do monitoring via USB or serial, you'd need to have a server/OS running with PCBE attached to each UPS. this may be cheaper in the long run but not physically feasible.

more expensively but a cleaner solution would be installing a [APC Network Management Card|http://www.apc.com/products/family/index.cfm?id=98] in each UPS so you can monitor each UPS via the network remotely. based on what you need, i recommend looking at AP9630. on the one server you want to shutdown, you can install the free Powerchute Network Shutdown and when installing the software, provide it the network address of the Network Management Card in the UPS it is attached to for power so that when the UPS is running low on battery or based on a specific configuration you complete, the NMC will send a shutdown signal over the network that the PCNS software will pick up and initiate a graceful shutdown on the server. PCNS also must be compatible with the server you are running for this to work. here is the compatibility chart -> http://www.apcmedia.com/salestools/SJHN-7AYQNP_R21_EN.pdf

hope this helps. i cant think of any other way to do what you need to unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore