None of the upsAdv OIS have anything there. A walk is empty.
Output:
1.3.6.1.4.1.318.1.1.1.3.3.4.0 (Gauge) = 499
1.3.6.1.4.1.318.1.1.1.4.1.1.0 (Integer32) = 2
1.3.6.1.4.1.318.1.1.1.4.1.2.0 (Integer32) = 3
1.3.6.1.4.1.318.1.1.1.4.2.1.0 (Gauge) = 240
1.3.6.1.4.1.318.1.1.1.4.2.2.0 (Gauge) = 49
1.3.6.1.4.1.318.1.1.1.4.2.3.0 (Gauge) = 36
1.3.6.1.4.1.318.1.1.1.4.2.4.0 (Gauge) = 40
1.3.6.1.4.1.318.1.1.1.4.2.5.0 (Gauge) = 3
1.3.6.1.4.1.318.1.1.1.4.2.6.0 (Integer32) = 80
1.3.6.1.4.1.318.1.1.1.4.3.1.0 (Gauge) = 2400
1.3.6.1.4.1.318.1.1.1.4.3.2.0 (Gauge) = 499
1.3.6.1.4.1.318.1.1.1.4.3.3.0 (Gauge) = 368
1.3.6.1.4.1.318.1.1.1.4.3.4.0 (Gauge) = 407
1.3.6.1.4.1.318.1.1.1.5.1.1.0 (Integer32) = 4
Firmware:
1.3.6.1.4.1.318.1.1.1.1.1.1.0 (OCTET STRING) = Symmetra 160K
1.3.6.1.4.1.318.1.1.1.1.1.2.0 (OCTET STRING) = SYMPX160
1.3.6.1.4.1.318.1.1.1.1.2.1.0 (OCTET STRING) = 560.0321.I
Any thoughts anyone? This is a BIG deal.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 09:29 PM . Last Modified: 2024-02-14 02:32 AM
I don't know much about this UPS but some thoughts:
- Which upsAdv OIDs are we discussing? Your walk has upsAdvOutput OIDs so I assume maybe we're talking about upsAdvInput I missed the title -- we're talking about upsAdvOutputActivePower.
Do any of your Symmetra 48k or 160k report upsAdvOutputActivePower now or in the past? As far as I can tell, it's not a measurement these UPSes support. The 160k and 48k often come with modular distribution which will report power on each breaker and subfeed under .1.3.6.1.4.1.318.1.1.22 (isxModularDistribution).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 09:29 PM . Last Modified: 2024-02-14 02:32 AM
I don't know much about this UPS but some thoughts:
- Which upsAdv OIDs are we discussing? Your walk has upsAdvOutput OIDs so I assume maybe we're talking about upsAdvInput I missed the title -- we're talking about upsAdvOutputActivePower.
Do any of your Symmetra 48k or 160k report upsAdvOutputActivePower now or in the past? As far as I can tell, it's not a measurement these UPSes support. The 160k and 48k often come with modular distribution which will report power on each breaker and subfeed under .1.3.6.1.4.1.318.1.1.22 (isxModularDistribution).