Multiple Power Supplies and Multiple UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Multiple Power Supplies and Multiple UPS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

0 Likes
4
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

Multiple Power Supplies and Multiple UPS

We're running a couple of servers, all equipped with dual power supplies. We have two UPSes powering all servers.

One each server, power supply A is connected to UPS A; and power supply B goes to UPS B. This creates a redundant power source in case an UPS fails.

The UPSes are connected to the network and we can monitor them through http.

We want to configure our network in order to have our UPSes send a signal to the servers so they can gracefully shut down during a power outage.

My worry is: is it possible to configure the servers (or the PowerChute agents) NOT to shutdown on the first shutdown signal? We don't want to have critical servers going down when a single UPS is failing and the network is still supposed to be runnning.

We want our servers to shut down when both UPSes are about to run out of batteries; not when one single UPS is failing and we still have facility power.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

0 Likes
1
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

you have to do it at least with the same TYPE of UPS - such as Smart UPS, Symmetra, etc. because i just dont think it is plain supported with different types of
UPSs through the software side of it - like using a Symmetra and Smart UPS.

futhermore, it is not recommended to do it with different models of Smart UPS or whatever UPS you have either because of the difference in load ratings, runtimes, etc - like if you used a Smart UPS 1000 and a Smart UPS 2200. obviously they will probably have different load ratings and one may run out of battery

by default, after doing a Custom Install on PCNS, the software will only shutdown after it receives the shutdown command from BOTH servers.

[see this article for exceptions and a little bit of other general info on this subject|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=3143]

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

0 Likes
0
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

PowerChute Network Shutdown can perform the shutdown needs that you are looking for.

With PCNS223 you can point to each UPS Network Management Card and the servers will only shut down when it sees a shutdown event you have configured occur on both UPS' for X amount of time (configurable on PCNS).

You can find the installation manual that includes instructions for a redundant UPS configuration here:
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SFPCNS223&tab=documentation

Please make sure that you are not using APC Network Card firmware v3.5.7 on your UPS systems as we have recently discovered that this can cause issues with PCNS functionality. Version 3.5.5 works perfectly fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

0 Likes
0
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

Hi there.
I got the message from support that we cannot do that when the kind of UPS are different.
Is it true? In our company we are using different model (all with management card). WE want to test it but at the moment we do not have a time for it. Is possible to configure one server and two different model’s UPS to shutdown the server (of course when the powers lose on both UPS).
Regards
Pawel

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

0 Likes
1
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

you have to do it at least with the same TYPE of UPS - such as Smart UPS, Symmetra, etc. because i just dont think it is plain supported with different types of
UPSs through the software side of it - like using a Symmetra and Smart UPS.

futhermore, it is not recommended to do it with different models of Smart UPS or whatever UPS you have either because of the difference in load ratings, runtimes, etc - like if you used a Smart UPS 1000 and a Smart UPS 2200. obviously they will probably have different load ratings and one may run out of battery

by default, after doing a Custom Install on PCNS, the software will only shutdown after it receives the shutdown command from BOTH servers.

[see this article for exceptions and a little bit of other general info on this subject|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=3143]

Reply

Link copied. Please paste this link to share this article on your social media post.

Teiger
Teiger
Cadet

Posted: ‎2023-11-21 03:47 AM

In response to BillP
0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-21 03:47 AM

The link in this solution is no longer valid. Can you please update?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of