Monitoring UPS data using SNMP OID
Dears.. I need to have the APC OID in this format 1.3.6.1.4.1.318.1.1.10.2.3.2.1.4.1 but every APC document has it in text like upsBasicTimeOnBattery and this is not working for me. so how can I get the numerical format for OIDs mentioned in "PowerNet Management Information Base (MIB) Version 3.4.4" document
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0801:51 AM. Last Modified: 2024-02-2910:30 PM
You could dig through the MIB, but it's easier to load it into a MIB browser. I use the free GetIF for Windows. Inside GetIF's program folder is a Mibs folder where you can put the MIB, and GetIF will show both the name and the numeric OID.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0801:51 AM. Last Modified: 2024-02-2910:30 PM
You could dig through the MIB, but it's easier to load it into a MIB browser. I use the free GetIF for Windows. Inside GetIF's program folder is a Mibs folder where you can put the MIB, and GetIF will show both the name and the numeric OID.