Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Missing SNMP values APC Smart-UPS 750

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Missing SNMP values APC Smart-UPS 750
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 12:38 AM . Last Modified: ‎2024-03-06 02:38 AM

0 Likes
6
5596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:38 AM . Last Modified: ‎2024-03-06 02:38 AM

Missing SNMP values APC Smart-UPS 750

Hello,

I'm trying to set up Nagios monitoring for an APC Smart-UPS 750 with a AP9630 network card. I found a really awesome tutorial with all the OIDs I could need here: [http://wiki.nagios.org/index.php/Howtos:snmp-apc-smart-ups] and set that up on a test machine but all of the tests came back saying that the OIDs don't exist. I initially figured that the OIDs in the tutorial were incorrect and grabbed the latest MIB from the APC website (powernet403.mib). I loaded it up in tkmib and found out that the OIDs were correct, however they are not returning any values. There is actually a large subtree which is inaccessible. Most of the values that I want have an OID that starts with .1.3.6.1.4.1.318.1.1.1, however walking it reveals only one value.

~$ snmpwalk -c (my community string) -v 1 (UPS IP) .1.3.6.1.4.1.318.1.1.1
SNMPv2-SMI::enterprises.318.1.1.1.8.1.0 = INTEGER: 2

I have enabled SNMPv1 in the settings and don't believe there are any network issues that could be causing the problem. The community string I'm using has read-only permissions. Is there something extra I need to configure to access this data? What could be causing this problem?

Thanks!

Sapphyre

tl;dr: APC Smart-UPS 750. AP9630 network card. Missing SNMP values in the .1.3.6.1.4.1.318.1.1.1 range. How do I get them?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • apc
  • communication
  • management
  • network
  • network_management_card
  • NMC
  • smart-ups
  • snmp
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:39 AM . Last Modified: ‎2024-03-06 02:37 AM

0 Likes
0
5596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:39 AM . Last Modified: ‎2024-03-06 02:37 AM

thanks !!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 12:38 AM . Last Modified: ‎2024-03-06 02:38 AM

0 Likes
0
5596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:38 AM . Last Modified: ‎2024-03-06 02:38 AM

Hi Sagervai,

>
tl;dr: APC Smart-UPS 750. AP9630 network card. Missing SNMP values in the .1.3.6.1.4.1.318.1.1.1 range. How do I get them?
>

A few points:
1. Make sure you install the latest version of the NMC firmware. The latest version as of writing is sumx515.
2. The PowerNet MIB describes OIDs used across all of our devices. To find the OIDs supported by a specific device, you'd need to walk the device as you have done. OIDs that don't show up are most likely not reported by your device.
3. In your case however, the one OID that shows up is upsCommStatus with the value "noComm". So I suspect the network management card isn't communicating with the UPS at all, so nothing shows up in SNMP. After making sure you have the latest firmware, check the web interface to make sure it's communicating with the UPS. Then try walking the device again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 12:38 AM . Last Modified: ‎2024-03-06 02:38 AM

0 Likes
0
5596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:38 AM . Last Modified: ‎2024-03-06 02:38 AM

I don't know if you're having the exact same problem as me, but I could not figure out where to input the SNMP values at the console prompt.  That's because you can't.

Once you give the card an IP address and make it available on the network, you have to then login through a web browser and enter the SNMP community strings there... under Administration - Network - SNMP - Access Control.

Good luck

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:38 AM . Last Modified: ‎2024-03-06 02:38 AM

0 Likes
0
5596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:38 AM . Last Modified: ‎2024-03-06 02:38 AM

In our next major firmware (v6.0.6) due out March 2013 (most likely next week) for AP9630/31 only with sumx and sy applications, we will be allowing for full SNMP configuration for v1/v3 at the console prompt via SSH/telnet. Today, on v5.X.X for AP9630/31/35, you can only enable/disable SNMP as Tim Smith just noted. Figured I'd mention it for anyone else who comes across this post when the new firmware is out for these applications or future applications that move to v6.0.X.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:39 AM . Last Modified: ‎2024-03-06 02:37 AM

0 Likes
0
5596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:39 AM . Last Modified: ‎2024-03-06 02:37 AM

how can i know if  this value:  upsAdvState Totaltime on battery: 1.3.6.1.4.1.318.1.1.1.11.2.7  is compatible with SUA750I? it doesn't return anything , that means that is incompatible?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 12:39 AM . Last Modified: ‎2024-03-06 02:37 AM

0 Likes
0
5596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:39 AM . Last Modified: ‎2024-03-06 02:37 AM

The only UPS that provides UPSAdvStateTotalTimeOnBattery is a Symmetra Megawatt system. The SmartUPS 750 doesn't provide it.

And yes, if the UPS does not respond to an SNMP OID, it means it's not supported. You can walk the UPS to determine which OIDs are supported.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:39 AM . Last Modified: ‎2024-03-06 02:37 AM

0 Likes
0
5597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:39 AM . Last Modified: ‎2024-03-06 02:37 AM

thanks !!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore