Dear All,
If any one know the solution of this below mention issue in symmetra PX 160 KVA UPS.
UPS is giving fault of Metering Board Issue whereas there is no metering Board is installed.because Symmetra PX UPS is install without Bypass Pannel ( Not using APC Bypass Pannel, and also not PDM,s )
Aftab
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:31 AM . Last Modified: 2024-03-19 12:45 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:31 AM . Last Modified: 2024-03-19 12:45 AM
Dear Aftab,
Please change your ups switch gar setting via display it should be none. your ups issue will resolve.
Regards,
Arif Hussain
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:31 AM . Last Modified: 2024-03-19 12:45 AM
See bottom of [this thread|http://forums.apc.com/spaces/11/netbotz-hardware-software/forums/general/7721/wacky-probe-notificati...].
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:31 AM . Last Modified: 2024-03-19 12:45 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:31 AM . Last Modified: 2024-03-19 12:45 AM
ho jay ga tension Q leta ha ..... zara APC se to in ko khap lenay do ... in ko b pata chalay k training lazmi hotee ha baqi jawab mil gaya ha es ka....
AJMAL
null
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:31 AM . Last Modified: 2024-03-19 12:45 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:31 AM . Last Modified: 2024-03-19 12:45 AM
Dear Aftab,
Please change your ups switch gar setting via display it should be none. your ups issue will resolve.
Regards,
Arif Hussain
Link copied. Please paste this link to share this article on your social media post.