Maximum Required Delay negotiation not working with any predictability (Symmetra RM, AP9631, PCNS)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Maximum Required Delay negotiation not working with any predictability (Symmetra RM, AP9631, PCNS)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
ben_m
Crewman ben_m
Crewman

Posted: ‎2024-12-10 04:54 PM . Last Modified: ‎2024-12-10 05:02 PM

0 Likes
0
335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-10 04:54 PM . Last Modified: ‎2024-12-10 05:02 PM

Maximum Required Delay negotiation not working with any predictability (Symmetra RM, AP9631, PCNS)

I have 3 x Symmetra RM w/ AP9631 NMC (firmware v6.2.1)

I am trying to set up automatic shutdown and startup using PCNS 5.1.0

 

Although I have a redundant setup in production, right now I am testing with just one UPS and one PCNS host, not in redundant mode.  Everything communicates fine, the shutdown sequence sort of works (all the things that are supposed to happen, do happen), but the timing isn't right at all.

 

When On Battery occurs, I want to wait 3 minutes, run a script for 5 minutes, shut down the PCNS machine (allowing 30 seconds for that), shut down load power, then shut down the UPS.

 

UPS should remain shut down for 60 seconds minimum even if power has returned, remain shut down until input power is on and fuel >= 50%, and then come back up and turn the load on.

 

THE PROBLEM: When I "Force Negotiation", I expect Maximum Required Delay to indicate 6 minutes. because in PCNS "On Battery Event" I have a command script time of 600 and a Shutdown Delay of 30.  This is 5:30, rounded up to the nearest minute == 6.

 

This does not happen, the Maximum Required Delay remains stubbornly at 2 minutes.

 

However, I noticed that if I increase Low Battery Duration, it increases Maximum Required Delay to the same value, eg 12 Minutes == 12 Minutes.  But my understanding is that low battery duration is the amount of (calculated) runtime remaining before shutdown occurs, so I don't understand why these settings interact?

 

I don't want my shutdown based on the calculated runtime, but just straightforwardly shut down based on the time elapsed since power failed.  I have done runtime calibration, and I have around 30 minutes of runtime.. whereas I will only be on battery for 10 minutes before shutting down...

 

MY SETTINGS ARE BELOW

 

My Settings in PCNS "On Battery" Event:

Enable Command File: Checked, Delay: 300 (max seconds script requires to run), Path to Command File is correct and works...

Enable Shutdown: Checked, Delay: 30,

 

NMC Shutdown Config

Low Battery Duration: 02 Minutes (the minimum)

Shutdown Delay: 120 Seconds (but I expect the PCNS config to override this)

Maximum Required Delay: 2 Minutes (But I expected this to be negotiated to at least 6 minutes)

Basic Signalling Shutdown: Unchecked

Controlled Early Shutdown, Nothing checked right now, since I am expecting PCNS to do this.

Sleep Time: 0.0

Minimum Battery Capacity: 50%

Return Delay: 060 Seconds

Maximum Required Delay:  2 Minutes (I expect this to be at least 6)

On-Battery Shutdown Behavior: Restart when power is restored

 

I should mention that the shutdown DOES run, and the UPS shuts down.  But I can't set the timings to what I want.  If I muck about with the delay settings in PCNS I can cause the Maximum Required Delay to change in the NMC, but not in a way I can replicate or predict, some settings work, others do nothing...

 

Please help, thanks!  I have been working at this for quite a while....

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • UPS Management Devices & PowerChute Software
  • Tags:
  • english
  • linux
  • NMC
  • pcns
  • PowerChute
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of