Maximum Required Delay Calculation

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Maximum Required Delay Calculation
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

0 Likes
4
2261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

Maximum Required Delay Calculation

Research on how the MRD is calculated indicates that the NMC polls connected PCNSs.

What setting does the NMC key off of?

I have a basic test environment with an SU1500 (w/AP9630) and a Win 2008 Server (PCNS 4.2.0).  No matter what changes I make in the PCNS settings the MRD remains the same as the Low Battery Duration set on the NMC.

Not sure if this is related, but the "Force negotiation" radio button does not remain selected under PowerChute Shutdown Parameters.

Thanks >> Joe

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • network-management-card
  • NMC
  • pcns
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

0 Likes
0
2261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

0 Likes
0
2261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

Hi,

The Maximum Required Delay is based on the greatest amount of time any registered PCNS client needs to complete the shutdown process. 

Example: there are 2 Windows server registered with AP9630 that is installed in SU model Smart-UPS. Each client is configured to start OS shutdown after the UPS has been on battery for 5 minutes. 1 of the clients is configured to run a command file prior to OS shutdown and that command file needs 4 minutes to complete it process.

When PCNS is restarted or when Force negotiation is selected and apply is clicked Maximum required delay is increased to 6 minutes Note: The changed can take up to 10 minutes when force negotiation is selected. 2 minutes for the default and 4 minutes for the command file delay. 

I recommend increasing the low battery threshold to be greater than the needed maximum required delay which will also increase the maximum required delay to match.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

0 Likes
0
2261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

Bill,

Thanks for the detailed answer.

We don't typically use Command Files but on more careful review it appears that is the only place where the PCNS can record a shutdown time requirement. We did try that setting but I thought the instructions indicated that the NMC should be rebooted.  I will go back and check.  We never tried restarting the PCNS.

Our Force Negotiation radio button does not stay selected when we hit apply. Is that normal?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

0 Likes
0
2260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

Hi,

On 5/26/2017 8:01 PM, Joe said:

Our Force Negotiation radio button does not stay selected when we hit apply. Is that normal?

Yes. The button reverts to unchecked after you click apply. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

0 Likes
0
2262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:12 AM . Last Modified: ‎2024-02-29 10:14 PM

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of