Maximum Life of an SYBT5 Lead-Acid battery module

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Maximum Life of an SYBT5 Lead-Acid battery module
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
michael.w.glaze
michael.w.glaze
Cadet

Posted: ‎2024-10-10 09:24 AM

0 Likes
1
256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-10 09:24 AM

Maximum Life of an SYBT5 Lead-Acid battery module

I am tasked with planning a budget for life-cycle replacement of my facilities UPS batteries. I have several UPS that use the SYBT5 battery module. I have only been able to find the minimum life (3yr) the warrantee duration (2yr) but not reference to a maximum or recommended replacement time? In my past experience with APC battery modules there was such a date. Is it now based on the voltage/load test results?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Spock Teken
Spock

Posted: ‎2024-10-11 05:43 AM

0 Likes
0
233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-11 05:43 AM

The average service life is stated as 2-5 years based on usage, temperature, and environmental conditions.

 

Generally speaking the battery replacement interval depends upon the level of conformance and standards you follow.

 

If this is a ISO / cUL certified site than the maintenance and change out interval is well defined for you and the site.

 

Especially if you conform and publish a uptime of service to your customers / public. ☝️

 

Regardless of all the above testing and validation of the system and batteries are the most basic requirements and tasks.

 

There is no other test in the industry that supersedes a (Lights Out / Grid Down) event!

 

This is either a pass / fail event . . . 

The only portion of the lights out test that is placed on a curve is the operational runtime when compared to the published APC Runtime Calculator for a specific load.

 

Meaning if the APC Runtime Calculator indicates a new cartridge can provide 60 minutes but you see 35-45 minutes.

 

Depending upon how stringent you follow your conformance you may let that slide vs ordering a hot spare immediately / a few months down. 

If the operational runtime was 5-10 minutes vs the 60. The battery cartridge needs to be replaced as it’s near end of life.

 

The internal resistance and load test are the primary factors that determine a battery pass / fail.

 

Measuring spot voltage offers very little information.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Teken
Spock Teken
Spock

Posted: ‎2024-10-11 05:43 AM

0 Likes
0
234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-11 05:43 AM

The average service life is stated as 2-5 years based on usage, temperature, and environmental conditions.

 

Generally speaking the battery replacement interval depends upon the level of conformance and standards you follow.

 

If this is a ISO / cUL certified site than the maintenance and change out interval is well defined for you and the site.

 

Especially if you conform and publish a uptime of service to your customers / public. ☝️

 

Regardless of all the above testing and validation of the system and batteries are the most basic requirements and tasks.

 

There is no other test in the industry that supersedes a (Lights Out / Grid Down) event!

 

This is either a pass / fail event . . . 

The only portion of the lights out test that is placed on a curve is the operational runtime when compared to the published APC Runtime Calculator for a specific load.

 

Meaning if the APC Runtime Calculator indicates a new cartridge can provide 60 minutes but you see 35-45 minutes.

 

Depending upon how stringent you follow your conformance you may let that slide vs ordering a hot spare immediately / a few months down. 

If the operational runtime was 5-10 minutes vs the 60. The battery cartridge needs to be replaced as it’s near end of life.

 

The internal resistance and load test are the primary factors that determine a battery pass / fail.

 

Measuring spot voltage offers very little information.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of