Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Maximum Life of an SYBT5 Lead-Acid battery module
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-1009:24 AM
Maximum Life of an SYBT5 Lead-Acid battery module
I am tasked with planning a budget for life-cycle replacement of my facilities UPS batteries. I have several UPS that use the SYBT5 battery module. I have only been able to find the minimum life (3yr) the warrantee duration (2yr) but not reference to a maximum or recommended replacement time? In my past experience with APC battery modules there was such a date. Is it now based on the voltage/load test results?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-1105:43 AM
The average service life is stated as 2-5 years based on usage, temperature, and environmental conditions.
Generally speaking the battery replacement interval depends upon the level of conformance and standards you follow.
If this is a ISO / cUL certified site than the maintenance and change out interval is well defined for you and the site.
Especially if you conform and publish a uptime of service to your customers / public. ☝️
Regardless of all the above testing and validation of the system and batteries are the most basic requirements and tasks.
There is no other test in the industry that supersedes a (Lights Out / Grid Down) event!
This is either a pass / fail event . . .
The only portion of the lights out test that is placed on a curve is the operational runtime when compared to the published APC Runtime Calculator for a specific load.
Meaning if the APC Runtime Calculator indicates a new cartridge can provide 60 minutes but you see 35-45 minutes.
Depending upon how stringent you follow your conformance you may let that slide vs ordering a hot spare immediately / a few months down.
If the operational runtime was 5-10 minutes vs the 60. The battery cartridge needs to be replaced as it’s near end of life.
The internal resistance and load test are the primary factors that determine a battery pass / fail.
Measuring spot voltage offers very little information.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-1105:43 AM
The average service life is stated as 2-5 years based on usage, temperature, and environmental conditions.
Generally speaking the battery replacement interval depends upon the level of conformance and standards you follow.
If this is a ISO / cUL certified site than the maintenance and change out interval is well defined for you and the site.
Especially if you conform and publish a uptime of service to your customers / public. ☝️
Regardless of all the above testing and validation of the system and batteries are the most basic requirements and tasks.
There is no other test in the industry that supersedes a (Lights Out / Grid Down) event!
This is either a pass / fail event . . .
The only portion of the lights out test that is placed on a curve is the operational runtime when compared to the published APC Runtime Calculator for a specific load.
Meaning if the APC Runtime Calculator indicates a new cartridge can provide 60 minutes but you see 35-45 minutes.
Depending upon how stringent you follow your conformance you may let that slide vs ordering a hot spare immediately / a few months down.
If the operational runtime was 5-10 minutes vs the 60. The battery cartridge needs to be replaced as it’s near end of life.
The internal resistance and load test are the primary factors that determine a battery pass / fail.
Measuring spot voltage offers very little information.