Max current through a 30A PDU

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Max current through a 30A PDU
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:31 PM

0 Likes
2
578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:31 PM

Max current through a 30A PDU

Hi all,

We've got a 30A drop into our cabinet and need to make the most of the available power. After speaking with the APC techs, it seems there is no good answer to just how much we can pull through our AP7932. The "Regulatory Derated Input Current" is 24A, I understand that's the NEMA derating to 80% of nominal. Still, leaving 20% of the available power on the table is just not going to cut it. Pretend that we can control spikes in current draw. Does anyone know how much we can reliably pull through this 80% solution before the breakers go POP and send us back to the stone age?

Are there any PDUs out there that will let us pull the full 30A?

Thanks,
Peter

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:10 AM . Last Modified: ‎2024-02-14 10:31 PM

0 Likes
0
578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:10 AM . Last Modified: ‎2024-02-14 10:31 PM

Not only that, it's a code. Anything that will operate for 3 hours or more is considered "continuous duty" and only allowed to use 80% of the capacity. Something like a hair dryer is considered "temporary". IT equipment are "continuous load".

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
K-Dog_apc
Lieutenant JG K-Dog_apc
Lieutenant JG

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:31 PM

0 Likes
0
578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:31 PM

Someone from APC will probably have to answer your question on the rack PDU but I would suggest the first bottleneck is the circuit breaker feeding the RPDU. If it is a typical installtion of a whip coming from a 20, 40 or 80kw Symmetra XPDU frame you are feeding it with a SquareD circuit breaker that is rated for 80% continuous duty. You might want to explore replacing this with a 100% rated cb assuming the RPDU is 100% continuous also. Having said that I have seen people run these breakers an amp or 2 over 100% rating for a long time but I would not recommend this under any circumstances. The safest solution from an uptime stand point would be to add a second RPDU for redundancy.

Message was edited by: K-Dog

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:10 AM . Last Modified: ‎2024-02-14 10:31 PM

0 Likes
0
579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:10 AM . Last Modified: ‎2024-02-14 10:31 PM

Not only that, it's a code. Anything that will operate for 3 hours or more is considered "continuous duty" and only allowed to use 80% of the capacity. Something like a hair dryer is considered "temporary". IT equipment are "continuous load".

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of