InRow RP Compressor Starting Up Every 5 Minutes

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • InRow RP Compressor Starting Up Every 5 Minutes
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:32 PM

0 Likes
2
647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:32 PM

InRow RP Compressor Starting Up Every 5 Minutes

I have a small data center consisting of:

Rack 1 - Radio control cabinet
Rack 2 - Battery rack
Rack 3 - Symmetra 20K
Rack 4 - Inrow RP
Rack 5 - Network/Switch cabinet, with ISX Management Module, Ethernet switch and various switches, bridges and routers.
Rack 6 - Server cabinet, with 6 servers, 5 rackmount, one freestanding on a shelf.

Rack 5 and 6 have temp sensors located on the front doors.

Group Setpoints:

Cool Setpoint and Supply Air are at 68 F
Humidify Setpoint is 45 % RH
Dehumidify Setpoint is 55 % RH
Dehumidify Deadband is 5 % RH
Reheat Setpoint is 64 F

Config is set to InRow

The InRow RP is cooling as it should, even moreso than expected. I am trying to determine why the compressor in the unit starts up about every 5 to 10 minutes. I've been told that the open spaces in each equipment rack need to be sealed off completely (we're getting the 200 piece airflow managment panel kit soon) to reduce the amount of cool air coming back into the InRow RP.

Any chance of reducing this startup and wear on the compressor, or will sealing the room a bit better and installing the airflow management panels reduce this occurrence?

Thanks,

Matt

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • compressor
  • cooling
  • inrow
  • rp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:31 PM

0 Likes
0
645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:31 PM

Matt,


Not sure if you're still lookin' for a reply, but one of our cooling techs was gracious enough to leave me an email pertaining to this:



The Inrow RP needs to be given a constant heatload of at least 10-12kW. If there is empty rack space without blanking panels, the cold air flowing to the hot aisle will reduce the heat load that the RP is given. With the supply air and cool setpoints both at 68F, you will likely see very high fan speeds. In the Inrow configuration, the supply air setpoint controls the temperature of the air the unit supplies to the cold aisle with compressor control. The cool setpoint controls the fan speed based on the maximum rack inlet temperature. The higher the rack inlet temperature is, the higher the fan speed will be (relative to the cool setpoint). These 2 setpoints should typically be 3-7F apart. In low load situations, the optimal setpoints often differ based on the specifc room configuration.


I would recommend setting the cool setpoint between 72-74F and monitoring the unit performance, adjusting the cool and supply air setpoints as needed. You can also enable the heat assist function. This will enable the unit to use the heater to help prevent excessive cycling (this can be enabled under "configure unit" on the front display or from the web interface under the unit tab, then the configuration section). Changing these settings and installing blanking panels will definitely help prevent cycling, but if the load is still too small then you may still have cycling issues. If you won't be getting blanking panels soon enough, you can use anything to block the airflow as a temporary blanking panel. If the compressor cycles 12 times within an hour it will go into an excessive compressor cycling alarm that has to be cleared manually. Regardless of whether or not it goes into the alarm, if you notice a large amount of cycling it is not good for the compressor life as you expected.




If you have any further questions on this, I would recommend contacting the Cooling ISX Tech Support Team via phone.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:32 PM

0 Likes
0
645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:32 PM

Hi Matt,

I asked one of our ISX Cooling team members to take a look at the thread yesterday (Friday the 20th). They're a little busy so apparently the gentleman did not get back to me in time before the end of my shift. I will shoot the entire team an email Monday (the 23rd) and see where we get.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:31 PM

0 Likes
0
646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:09 AM . Last Modified: ‎2024-02-14 10:31 PM

Matt,


Not sure if you're still lookin' for a reply, but one of our cooling techs was gracious enough to leave me an email pertaining to this:



The Inrow RP needs to be given a constant heatload of at least 10-12kW. If there is empty rack space without blanking panels, the cold air flowing to the hot aisle will reduce the heat load that the RP is given. With the supply air and cool setpoints both at 68F, you will likely see very high fan speeds. In the Inrow configuration, the supply air setpoint controls the temperature of the air the unit supplies to the cold aisle with compressor control. The cool setpoint controls the fan speed based on the maximum rack inlet temperature. The higher the rack inlet temperature is, the higher the fan speed will be (relative to the cool setpoint). These 2 setpoints should typically be 3-7F apart. In low load situations, the optimal setpoints often differ based on the specifc room configuration.


I would recommend setting the cool setpoint between 72-74F and monitoring the unit performance, adjusting the cool and supply air setpoints as needed. You can also enable the heat assist function. This will enable the unit to use the heater to help prevent excessive cycling (this can be enabled under "configure unit" on the front display or from the web interface under the unit tab, then the configuration section). Changing these settings and installing blanking panels will definitely help prevent cycling, but if the load is still too small then you may still have cycling issues. If you won't be getting blanking panels soon enough, you can use anything to block the airflow as a temporary blanking panel. If the compressor cycles 12 times within an hour it will go into an excessive compressor cycling alarm that has to be cleared manually. Regardless of whether or not it goes into the alarm, if you notice a large amount of cycling it is not good for the compressor life as you expected.




If you have any further questions on this, I would recommend contacting the Cooling ISX Tech Support Team via phone.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of