Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Many "Communications lost" messages in event log of AP8641

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Many "Communications lost" messages in event log of AP8641
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
jmbarker
jmbarker
Cadet

Posted: ‎2024-02-22 06:04 PM

0 Likes
1
646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-22 06:04 PM

Many "Communications lost" messages in event log of AP8641

This PDU was previously connected to a network of multiple PDUs, and is now being used independently. After disconnecting for a few months and now setting it up again, many error messages like the following appear in the event log:

 

 

Rack PDU 1: Component communications lost with Outlet Board 3 Meter.  Please verify that a terminator is inserted in either the In or Out port.
Rack PDU 1: Component communications lost with Outlet Board 2 Meter.  Please verify that a terminator is inserted in either the In or Out port.
Rack PDU 1: Component communications lost with Outlet Board 1 Meter.  Please verify that a terminator is inserted in either the In or Out port.
Rack PDU 1: Communications lost.
Rack PDU 1: Component communications lost with Phase Meter.

 

 

All monitoring reads 0 both from the Web UI and the display on the unit. I have tried attaching the terminator to both the IN and OUT ports (individually), with no difference. I have not tried running the unit without the terminator installed, nor have I tried two terminators or a different terminator (I only have one available).

 

I have tried re-seating the display connector, as well as the other three connectors under the display. No components on the boards look obviously damaged, nor do any of the internal wires. I updated the firmware to the latest version (7.1.3) successfully, with no change in behaviour. I reset the device to factory defaults, with no change in behaviour.

 

Are there any further troubleshooting steps I can take? This device worked perfectly 6 months ago, and nothing has changed except for being powered off during that time and no longer being connected to other PDUs.

 

I have attached the result of About->Support->Generate Logs, hopefully that will be of further help.

Attachments
debug_ZA1450013801.7z
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Kirk Teken
Kirk

Posted: ‎2024-04-04 07:54 AM

0 Likes
0
576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-04 07:54 AM

You have completed all of the relevant troubleshooting steps besides swapping the display with another to see if the problem follows the display to another PDU.

 

If you take a good working display and insert it into the trouble PDU and you see a fault it’s the PDU. If however the (swapped) display operates fine you at least know the PDU is also not at fault.

 

NEXT: Taking the problem display to a fully working & functional PDU. If the issue persists the display is faulty and needs to be repaired / replaced.

 

Let me know what you find and the break fix. If this feedback is relevant and on point mark this as solved. 👍🍺

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore