Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Easy UPS E3SUPS10KHB Alarma "Cabl paralelo incorrecto"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Easy UPS E3SUPS10KHB Alarma "Cabl paralelo incorrecto"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
hernan.gesueli
hernan.gesueli
Contributor

Posted: ‎2024-03-23 08:03 AM

0 Likes
2
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-23 08:03 AM

Easy UPS E3SUPS10KHB Alarma "Cabl paralelo incorrecto"

Buenos días.

Tengo una Easy UPS s 3:3 de 10 kVA con baterías internas.

El equipo se puso en marcha hace más de un mes, y esta semana aparece en alarma con el mensaje "Cabl paralelo incorrecto". El equipo es SINGLE sin paralelo, no forma parte de una instalación en paralelo y no tiene cables conectados en el puerto del paralelo. En el Event Log no aparece el evento con la fecha y hora de activación de la alarma. No puedo acceder al árbol de menú "System Mode" para visualizar la configuración, la cuál no fue modificada de como viene por Default de fábrica (viene en "SINGLE") y tampoco acceder para modificar la configuación.

¿Cómo se puede eliminar la alarma y verificar que la configuración de "System Mode" esté en "Single"?

 

hernangesueli_0-1711206149222.png

hernangesueli_1-1711206166831.png

 

Muchas gracias!!!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
hernan.gesueli
hernan.gesueli
Contributor

Posted: ‎2024-04-05 04:56 AM

In response to Teken
0 Likes
0
1338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-05 04:56 AM

Buenos días.

 

La semana pasada nos copartieron un software denominado Tuner para Easy UPS, con el mismo pudimos conectarnos localmente con el cable de consolta, bajar un Log de información llamado Report e ingresar al parámetro "System Mode" de la UPS, modificando el mismo de "Paralelo" a "Single". El tema fue resuelto con soporte de Schneider Argentina.

 

Muchas gracias.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Teken
Teken
Champion

Posted: ‎2024-04-04 07:33 AM

0 Likes
1
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-04 07:33 AM

What happens when you enter the settings password?!? Assuming it hasn’t been changed it’s: 3526

 

Given this unit is still under APC warranty and support you should contact them directly to help resolve this issue. There are options greyed out that you can not change or modify without APC providing the restricted code.

 

Please do let us know if the access code I provided helps resolves your problem. Or if you needed APC support to solve the same and what the solution was.

 

If my feedback resolved your problem insure you mark this as solved. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

hernan.gesueli
hernan.gesueli
Contributor

Posted: ‎2024-04-05 04:56 AM

In response to Teken
0 Likes
0
1339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-05 04:56 AM

Buenos días.

 

La semana pasada nos copartieron un software denominado Tuner para Easy UPS, con el mismo pudimos conectarnos localmente con el cable de consolta, bajar un Log de información llamado Report e ingresar al parámetro "System Mode" de la UPS, modificando el mismo de "Paralelo" a "Single". El tema fue resuelto con soporte de Schneider Argentina.

 

Muchas gracias.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore