Maintenance, Shutdown - execution order.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Maintenance, Shutdown - execution order.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:43 AM . Last Modified: ‎2024-02-29 10:35 PM

0 Likes
1
720
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:43 AM . Last Modified: ‎2024-02-29 10:35 PM

Maintenance, Shutdown - execution order.

Hello

Our enviroment is: 4 Esxi 6.0 hosts in vCenter cluster (with DRS enabled)  + fresh install of PowerChute 4.1 Vappliance + 1 APC SMART-UPS VT 15 kVA
PCNS is configured to shut down VMs on "on battery event"  but we do not want VM to be migrated (migration on PCNS is disabled)

Everything would work just fine if not one exeption.
1. If "on battery event" occurs PCNS trying to put all host in maintenance mode.
2. Because of maintanace mode  DRS is trying to migrate VMs as quick as possible to any avaliable host.
3. Because hosts are being put into maitanace sequentially (not all at the same time) - VM's are starting to migrate crazy over whole enviroment.

So there are lots of migration going on - but not shuting down.  Eventually all VM's will be shut, but is this "migration confusion" really necessary ?

Am'I missing an idea of network shutdown or do we have some inproper settings in PCNS ?Should't PCNS shutdown VM at a first place and then try to put host in maintenance ?

How we should set our envirometn (VMware + PCNS) to prevent from migrating during shutdown sequence ?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • maintenance
  • order
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:43 AM . Last Modified: ‎2024-02-29 10:35 PM

0 Likes
0
720
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:43 AM . Last Modified: ‎2024-02-29 10:35 PM

Tom,

if you do not want the VMs migrated you need to disable DRS or create a DRS rule that would cause the VMs to be migrated to 1 of the host that are being put into maintained mode which should prevent the migration. 

VM migration with DRS is discussed starting on page 29 of the user’s guide.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:43 AM . Last Modified: ‎2024-02-29 10:35 PM

0 Likes
0
721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:43 AM . Last Modified: ‎2024-02-29 10:35 PM

Tom,

if you do not want the VMs migrated you need to disable DRS or create a DRS rule that would cause the VMs to be migrated to 1 of the host that are being put into maintained mode which should prevent the migration. 

VM migration with DRS is discussed starting on page 29 of the user’s guide.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of