Mac Mini OSX 10.7 Server UPS Solution?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Mac Mini OSX 10.7 Server UPS Solution?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

0 Likes
4
1036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

Mac Mini OSX 10.7 Server UPS Solution?

Hi all,
We are migrating from our old Xserve G5 servers to new Mac Mini OSX 10.7 servers. We currently have a Smart UPS 1000XL.

1. Can we use the existing UPS with the new Mac Mini Servers?

2. If so, is a serial-to-usb cable needed? What Powerchute software version is needed?

3. If not, what is the appropriate UPS solution that would allow the Mac Mini Servers to shut down properly during a power failure?

If anyone has any info on these questions, your input would be greatly appreciated.

Thanks
KC

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

0 Likes
0
1036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

Hello kcaldera,

You pretty much nailed it, Yes that's how the NMC or the AP9630 works with the Powerchute Network Shutdown client that you'll install on the servers. For example, when the UPS goes on battery and then reaches the low battery warning, the NMC send out a shutdown broadcast to the network to be received by the servers running PCNS which then in turn gracefully shuts down the server
*Here's how to configure the NMC's TCP/IP settings.
*FAQ for PCNS 3.0
*[PowerChute Network Shutdown v3.0 - Installation and Configuration Guides|http://www.apcmedia.com/salestools/PMAR-8EMDEM_R0_EN.pdf]


I hope this helps!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

0 Likes
0
1036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

Joe, Kulot,
Thank you'll very much for your time and help. It is much appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

0 Likes
0
1036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

Your Smart-UPS should have an option for USB communication. In that case, connect it to your Mac mini via USB and your Mac will automatically configure itself to communicate with the UPS. You will see a battery icon up in the menu bar near the clock. You can also configure the UPS related behavior via the Energy Saver preference pane under System Preferences.

APC does not support any version of Mac OS X from 10.5 Leopard to 10.7 Lion, since the built-in "native" support provides the basic functionality without additional 3rd party software.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

0 Likes
0
1036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

So, my boss wants us to have the capability of shutting down multiple servers with this one UPS.

Smart-UPS1000XL.

From reading the online docs, here is what I figure needs to happen, please correct me if I miss anything...

1. We need to purchase an AP9630 NMC to install in the 1000XL.
2. Configure the NMC with appropriate IP and so on.
3. Install PCNS v3 software for Mac on each servers.
4. Point the PCNS to the IP address of the NMC.

Is this correct? Since I don't have screen shots..I believe PCNS on the server is simply watching for any warning packets coming from the NMC's IP address. Then when each server receives such packets, it starts the shutdown process.... Is this right?

Thanks for your time, it is much appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

0 Likes
0
1037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:28 AM . Last Modified: ‎2024-03-11 02:35 AM

Hello kcaldera,

You pretty much nailed it, Yes that's how the NMC or the AP9630 works with the Powerchute Network Shutdown client that you'll install on the servers. For example, when the UPS goes on battery and then reaches the low battery warning, the NMC send out a shutdown broadcast to the network to be received by the servers running PCNS which then in turn gracefully shuts down the server
*Here's how to configure the NMC's TCP/IP settings.
*FAQ for PCNS 3.0
*[PowerChute Network Shutdown v3.0 - Installation and Configuration Guides|http://www.apcmedia.com/salestools/PMAR-8EMDEM_R0_EN.pdf]


I hope this helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore