Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

MGE Galaxy PW 225KVA UPS and SNMP OID .1.3.6.1.4.1.705.1.4.1.0

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • MGE Galaxy PW 225KVA UPS and SNMP OID .1.3.6.1.4.1.705.1.4.1.0
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
troyb
troyb
Cadet

Posted: ‎2021-12-02 03:39 PM

0 Likes
1
1051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-02 03:39 PM

MGE Galaxy PW 225KVA UPS and SNMP OID .1.3.6.1.4.1.705.1.4.1.0

Hello everyone,

 

I have a question about the following SNMP OID. The MIB does not provide much detail on what exactly it does or is used for.

 

OID: .1.3.6.1.4.1.705.1.4.1.0

OID Name: upsmgConfigBatteryInstalled

 

Presently both our units show that this is coming up as "no(2)" and the description is "The battery installed status". Now I know batteries are installed in these units. 80 batteries each unit to be exact and they do carry the load when there is a power outage.

 

So my question is what exactly does this OID do and will it cause any issues if I set it to "yes(1)"?  I understand that the value is actually 1 or 2, but just providing the MIB presented values.

 

Thanks for taking a look and assisting.

 

Best,

 

-Troy

Labels
  • Labels:
  • Datacenter UPS
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
StacyC
Crewman StacyC Crewman
Crewman

Posted: ‎2021-12-08 06:26 AM

0 Likes
0
1022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-08 06:26 AM

Hi Troy,

 

That section of the MIB is configuration of the UPS and cannot be configured from SNMP or Modbus.  A Field Service Engineer (FSE) has to connect to the UPS to configure the setting to you are asking about.  I recommend having the FSE review the configuration on the next maintenance visit.  You state that the UPS hold the load on battery, so the UPS is function normally.  If the UPS display shows the correct runtime or battery percentage then the battery information in the UPS is configured but that setting might have been missed.  If you do not have correct runtime or no runtime then the battery information is not configured in the UPS and should be reviewed by a FSE.  Presently I don’t see any issue as the UPS functions correctly on battery.

 

Best regards,

Stacy

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of