Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Dusting SYPM10KF power modules from a Symmetra PX

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Dusting SYPM10KF power modules from a Symmetra PX
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
159
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
ojfsdi
ojfsdi
Contributor

Posted: ‎2021-11-16 08:48 PM

0 Likes
3
2384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-16 08:48 PM

Dusting SYPM10KF power modules from a Symmetra PX

I've got a Symmetra PX 80kw with qty 9 10kw power modules.  They're all pretty dusty.

 

I'd like to clean them up before they fail from dust accumulation.

 

How long after pulling them free of their bus bars should I wait before dusting them?

 

I'm particularly concerned about the large capacitors having time to bleed down.

 

Is there an official method to discharge them in a controlled manor?

 

I don't want dust creating a short when I'm trying to clean them and causing a short and damaging a circuit board or soiling my pants.  I'd also like to safe all surfaces internally to touch if possible, to permit a more thorough cleaning and inspection

Labels
  • Labels:
  • Datacenter UPS
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ojfsdi
ojfsdi
Contributor

Posted: ‎2021-12-04 08:22 PM . Last Modified: ‎2021-12-04 08:35 PM

In response to al_buffington
0 Likes
1
2326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-04 08:22 PM . Last Modified: ‎2021-12-04 08:35 PM

Interesting you say that.  Schneider might want to tell whoever it is that manufacturers the modules then.  Because the manufacturer left a little sticker for the customer that talks specifically about the opening of power modules for servicing and states how long I should wait.  I feel pretty silly I didn't notice this earlier!

 

PXL_20211120_072727638(2).jpg

 

So. the answer to this one is:

APC says to wait 5 minutes after removing a Power Module, before opening that module.

 

I'll also note, for the benefit of fellow Symmetra owners, I have successfully used an air compressor to dust all Power Modules (one by one while they were outside the Frame)  It could take several minutes to remove all dust.

 

There may be areas on the circuit board where it looks like some sort of oil has spilled out, but it might not be oil, rather just dust that has really settled down.  It may be removable with the electronics cleaner "I.D. Red" by Zep.    Apply Red with one hand, and immediately after, while its still "wet", hit it with high pressure air from the compressor to remove the detritus that Red has loosened. Wear eye protection.

 

I did have to change the positioning of the power module during cleaning, from laying normally, to laying on each side, several times because there are places the heavier chunks of dust will settle on the sides that don't blow out when it's just sitting normally.  It of course needs to be held when it's on edge so it doesn't fall over.

 

Don't forget to dust on both sides of the black plastic insulator sheets.  Wash the lid with a wet rag separately from the module and its electronics.

 

Allow sufficient time for Red (and any moisture in the air hose) to evaporate before reinstalling the module, and I haven't had any problems from the cleaning process as described.  Hope this helps someone out there.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
al_buffington
al_buffington Contributor
Contributor

Posted: ‎2021-11-18 02:03 PM

0 Likes
2
2370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-18 02:03 PM

Hi,

 

For safety reasons, there is no procedure for customers to clean or service their own systems. Power Modules should only be opened by Schneider authorized field service representatives.  

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ojfsdi
ojfsdi
Contributor

Posted: ‎2021-12-04 08:22 PM . Last Modified: ‎2021-12-04 08:35 PM

In response to al_buffington
0 Likes
1
2327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-04 08:22 PM . Last Modified: ‎2021-12-04 08:35 PM

Interesting you say that.  Schneider might want to tell whoever it is that manufacturers the modules then.  Because the manufacturer left a little sticker for the customer that talks specifically about the opening of power modules for servicing and states how long I should wait.  I feel pretty silly I didn't notice this earlier!

 

PXL_20211120_072727638(2).jpg

 

So. the answer to this one is:

APC says to wait 5 minutes after removing a Power Module, before opening that module.

 

I'll also note, for the benefit of fellow Symmetra owners, I have successfully used an air compressor to dust all Power Modules (one by one while they were outside the Frame)  It could take several minutes to remove all dust.

 

There may be areas on the circuit board where it looks like some sort of oil has spilled out, but it might not be oil, rather just dust that has really settled down.  It may be removable with the electronics cleaner "I.D. Red" by Zep.    Apply Red with one hand, and immediately after, while its still "wet", hit it with high pressure air from the compressor to remove the detritus that Red has loosened. Wear eye protection.

 

I did have to change the positioning of the power module during cleaning, from laying normally, to laying on each side, several times because there are places the heavier chunks of dust will settle on the sides that don't blow out when it's just sitting normally.  It of course needs to be held when it's on edge so it doesn't fall over.

 

Don't forget to dust on both sides of the black plastic insulator sheets.  Wash the lid with a wet rag separately from the module and its electronics.

 

Allow sufficient time for Red (and any moisture in the air hose) to evaporate before reinstalling the module, and I haven't had any problems from the cleaning process as described.  Hope this helps someone out there.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

al_buffington
al_buffington Contributor
Contributor

Posted: ‎2021-12-07 06:40 AM

In response to ojfsdi
0 Likes
0
2309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-07 06:40 AM

Hi,

 

The presence of the label is not an invitation for customers to open the power module. SE/APC places this label, or some variation of it, on many (probably all) of its three phase power modules. It is required for UL1778 certification. The only individuals that should open modules are authorized field service engineers and/or factory repair technicians. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore