Posted: 2021-06-26 05:44 AM . Last Modified: 2024-03-19 12:36 AM
MGE Galaxy 3000 & PCNS 3.0.1
Hello,
is it possible to configure PCNS to work together with an MGE Galaxy 3000?
If so, how to?
Thanks for help.
Best regards,
APCUserBav
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:44 AM . Last Modified: 2024-03-19 12:36 AM
It's a mistake......
- Galaxy 3000 use 66074 NMC card and Network Shutdown Module software
- Galaxy 300 use AP963x NMC card and Power Shute Network Shutdown software
And the support for G300 was added into PCNS 3.0.x
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:44 AM . Last Modified: 2024-03-19 12:36 AM
hello. unfortunately PCNS will not work with this UPS. The only option I am aware of would be the MGE NMC and MGE Network Shutdown Module. Did an NMC come with this UPS?
For reference, we currently only support Galaxy 3500/7000/300 with PCNS.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:44 AM . Last Modified: 2024-03-19 12:36 AM
i have a feeling it should read 300 and not 3000 unfortunately. let me go and check with who made the document.
EDIT I just found a current revision and it appears to be corrected: http://www.apcmedia.com/salestools/SJHN-8HDKQT_R1_EN.pdf
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:44 AM . Last Modified: 2024-03-19 12:36 AM
Hello,
thanks for responding.
The attached .pdf says, Support for Galaxy 3000 was added in Version 3.0.0.
Was it removed in 3.0.1?
Best regards.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:44 AM . Last Modified: 2024-03-19 12:36 AM
It's a mistake......
- Galaxy 3000 use 66074 NMC card and Network Shutdown Module software
- Galaxy 300 use AP963x NMC card and Power Shute Network Shutdown software
And the support for G300 was added into PCNS 3.0.x
Link copied. Please paste this link to share this article on your social media post.