MGE GALAXY 20 AND 80kVA UPS does need Service Bypass Panel to become Parallel Redundant???

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • MGE GALAXY 20 AND 80kVA UPS does need Service Bypass Panel to become Parallel Redundant???
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

0 Likes
6
809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

MGE GALAXY 20 AND 80kVA UPS does need Service Bypass Panel to become Parallel Redundant???

Dear All,

Can any body tell me does MGE GALAXY 20 and 80kVA Ups's must need Service bypass panel to become parallel redundant? If I would like to run two OR  three 20/20 kVA UPS 's without SBP then can it possible? and the same question is for 80kVA ups's???

I will wait for your responses.

Thanks a lot in advance.

War

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

0 Likes
0
808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

Angela You know if we compare our APC Ups's to  Eaton PowerWare the main difference is that Eaton gives every type of customization with their ups's. They generally do not use SBP and with their customized parallel kits they can parallel not only 2, but 3, 4, 5, 6.... so on.

You see in our parallel kits there is not a Jack for the third ups. Therefore if our customer wants to get paralleled their 3 ups's they simply can not. But in Eaton they can easily. I think this is a heavy draw back.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

0 Likes
0
808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

Dear All,

Can any body tell me does MGE GALAXY 20 and 80kVA Ups's must need Service bypass panel to become parallel redundant? If I would like to run two OR  three 20/20 kVA UPS 's without SBP then can it possible? and the same question is for 80kVA ups's???

I will wait for your responses.

Thanks a lot in advance.

War

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

0 Likes
0
808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

You're question is a bit vague as far as the exact model/SKUs so here is the best I can give you without knowing further details:

The Galaxy 3500 20KVA Single Phase output UPS can only be paralleled by using a purpose built APC SBP (SBPAR3I15K20R2M2-WP). The UPSs must be the same model (KVA rating) in order to accomplish this. Only two single phase UPS's can be paralleled together.

The Galaxy 3500 20KVA 3 phase output UPS can only be paralleled using a purpose built APC SBP (use SBPAR10K20H-WP  for up to 3 UPSs) contact APC if you require a panel for 4 parallel units). Again the UPS's must be the same model number (KVA rating) and you can parallel up to 4 UPSs.

If you're referring to a Galaxy 300 UPS, then 2 units can be paralleled using a parallel kit: G3HTPARKITS, no need for a seperate SBP.

If you're referring to the Galaxy 5500 80KVA UPS then these can be paralleled up to a maximum of 6 units (only 4 units if he is to use an external bypass panel).

So again, since there are several Galaxy 20 & 80 KVA units out there,  which UPS are you referring to so that we can give you more relevant details.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

0 Likes
0
808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

Dear Angela,

Asusual, What a great, detailed neat and clean reply from your side.


Please see the following,

Firstly, I am referring 3 phase In and 3 phase out ups's.

Secondly, as you say, If you're referring to a Galaxy 300 UPS, then 2 units can be paralleled using a parallel kit: G3HTPARKITS, no need for a seperate SBP.  My question is If i wanna run 3 or 4 galaxy ups's (300 series, 20kVA) then it can run without SBP only using parallel kit? simply, how many same rating ups's i can run without SBP??

Lastly, For mge galaxy 5500 series 80kVA UPS'S ,  What I understand, You say that,  maximum 6 units can be paralleled but only 4 units can be paralleled without SBP but for 6 units we would have to use SBP right?

Will wait for your response.

Thanks again.

War

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

0 Likes
0
808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

Here is additional feedback from our 3 phase EMEA support:

Firstly, I am referring 3 phase In and 3 phase out ups's.

Secondly, as you say, If you're referring to a Galaxy 300 UPS, then 2 units can be paralleled using a parallel kit: G3HTPARKITS, no need for a seperate SBP.  My question is If i wanna run 3 or 4 galaxy ups's (300 series, 20kVA) then it can run without SBP only using parallel kit? simply, how many same rating ups's i can run without SBP??

The limitation is 2 X UPSs in parallel. The parallel capability of the Galaxy 300 allows up to 2 units to be run in parallel (3:3 version only) for increased redundancy. All UPSs must be the same kVA rating.

Lastly, For mge galaxy 5500 series 80kVA UPS'S ,  What I understand, You say that,  maximum 6 units can be paralleled but only 4 units can be paralleled without SBP but for 6 units we would have to use SBP right?

You may find the guide below of interest to you as it explains the various configurations of our UPS's.

http://www.apcmedia.com/salestools/LARD-8YPBGX/LARD-8YPBGX_R0_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

0 Likes
0
808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

OK...... Got it.

Given literature is very interesting and good.

Thank u dear for the help as always.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

0 Likes
0
809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:59 AM . Last Modified: ‎2024-03-19 12:24 AM

Angela You know if we compare our APC Ups's to  Eaton PowerWare the main difference is that Eaton gives every type of customization with their ups's. They generally do not use SBP and with their customized parallel kits they can parallel not only 2, but 3, 4, 5, 6.... so on.

You see in our parallel kits there is not a Jack for the third ups. Therefore if our customer wants to get paralleled their 3 ups's they simply can not. But in Eaton they can easily. I think this is a heavy draw back.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore