Good afternoon everyone.
Is this normal, with the factory settings of the APC Easy-UPS SMV3000CA UPS, the decrease goes from 240 Volts (when the network is more than 230 Volts, namely 240 Volts) to 202-203 Volts (I did not believe the program, I measured it with a tester, the UPS actually gives 202-203 Volt when working on a decrease), as for me, this is a very low voltage ... Is this the norm? How do I regulate this?
The UPS costs 53,000 rubles, which is just nonsense. IMHO. Give answer?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:14 AM . Last Modified: 2024-03-07 11:21 PM
It will do this if you have configured it to. Personally I think 240 V is fine (it is what comes out of the wall here) so I configure mine to only drop the voltage once it goes above 250 V, and then it drops it back to around 210-220 V.
It is supposed to be based around some rule where it is maintaining +/- 20% of the nominal voltage, so if yours is set to 220 V then 240 V is probably too high, but 202 V isn't so bad. Either way these values can be configured so you can change them if you wish.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:14 AM . Last Modified: 2024-03-07 11:21 PM
It will do this if you have configured it to. Personally I think 240 V is fine (it is what comes out of the wall here) so I configure mine to only drop the voltage once it goes above 250 V, and then it drops it back to around 210-220 V.
It is supposed to be based around some rule where it is maintaining +/- 20% of the nominal voltage, so if yours is set to 220 V then 240 V is probably too high, but 202 V isn't so bad. Either way these values can be configured so you can change them if you wish.