Low Battery Messages when they Seem to be OK

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Low Battery Messages when they Seem to be OK
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:31 AM

0 Likes
6
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:31 AM

Low Battery Messages when they Seem to be OK

Low Battery Messages when they Seem to be OK
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:31 AM

0 Likes
0
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:31 AM

Just a thought but if it happened after a power outage, perhaps the alert started when the battery became discharged and never properly cleared. If that's the case, restarting the NMC would clear up the alert. It shouldn't do that, but if you find rebooting the NMC clears the problem, let us know.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:31 AM

0 Likes
0
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:31 AM

Coincidentally, I am experiencing a similar issue with my SMX1500rm2u.  The load is quite low, around 3.5 amps, battery is at 100 percent, the UPS passes self-test without an issue and, still, when I login to the NMC2 I have a boat-load of those messages.

My UPS indicates that the next scheduled battery change is due in a few weeks yet there is no real indication of imminent battery failure.  I may try a calibration test to run the batteries down to near failure and see if that resolves anything.  Other than that, I am looking for a replacement battery because they are probably near their EOL.

I'll watch this thread with interest.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:31 AM

0 Likes
0
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:31 AM

I was able to prevent the messages from happening by simply resetting the "battery installation date" via the NMC web interface in the "configuration/ups" drop down.  Apparently, if the battery replace-by date has passed even though the batteries are still good, the messages will be produced.

That being said, I did order a new RBC115 from a local vendor just to be on the safe side.

If someone from APC could confirm that this sort of message is also used for alerting the user that a battery is due to be replaced would be beneficial.  Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:31 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:31 AM

Just a thought but if it happened after a power outage, perhaps the alert started when the battery became discharged and never properly cleared. If that's the case, restarting the NMC would clear up the alert. It shouldn't do that, but if you find rebooting the NMC clears the problem, let us know.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:31 AM

0 Likes
0
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:31 AM

Hi Voidstar,

In my case, resetting the battery install date forward to today's date eliminated the low battery messages.  I confirmed that this is apparently a "nanny-gram" sort of message as I set the battery install date to a point more than five (5) years ago and the low battery messages started up again but only when the load on the UPS was around 45%.

That being said, I am not sure how the Sean, the OP, is doing with his issue.  I hope he lets us know.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:31 AM

0 Likes
0
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:31 AM

Some of the newer UPSes have battery lifetime warning alarms that attempt to estimate the lifespan of the battery based on usage and temperature. Changing the install date would make those go away and also reset the UPS's runtime estimation parameters. The battery discharged alarm mentioned in the original post (OP) is only supposed to depend on runtime, which the OP's UPS seemed to have plenty of.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:30 AM

0 Likes
0
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:30 AM

Voidstar, that worked fantastically. The old error must have stuck in the NMC and wouldn't let go. 

A reboot of the NMC fixed the problem for me.

Thanks!

Sean

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore