Lost Communication to the UPS after firmware update

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Lost Communication to the UPS after firmware update
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
NikSpasov
Crewman NikSpasov
Crewman

Posted: ‎2022-01-17 08:59 AM

0 Likes
4
4586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-17 08:59 AM

Lost Communication to the UPS after firmware update

Hello,

I have APC Smart-UPS 2200VA LCD 230V (SMT2200I) with AP9631 and before the firmware update, everything was fine.

After the update, I have "Lost Communication to the UPS".

 

 

Could you help me, please?

Thanks,
Nik

 

Screenshot 2022-01-17 185229.jpg

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Shaun
Commander Shaun Commander
Commander

Posted: ‎2022-01-17 09:14 AM

0 Likes
2
4574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-17 09:14 AM

Hi @NikSpasov,

 

Thanks for the screenshot, it makes getting to the issue much easier - the screenshot shows the firmware loaded is "sy3p", which is for 3-Phase Symmetra UPS - so the card is complaining because it's trying to speak to a Symmetra, and a Symmetra isn't answering.

 

The current firmware for your UPS would be https://www.se.com/ie/en/product/SFSUMX704/ups-network-management-card-v7-0-4-firmware-for-smartups-...

 

As the card still appears to be on the network, recovery should be as simple as loading the correct firmware.

 

Regards,

  Shaun

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Shaun
Commander Shaun Commander
Commander

Posted: ‎2022-01-17 09:14 AM

0 Likes
2
4575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-17 09:14 AM

Hi @NikSpasov,

 

Thanks for the screenshot, it makes getting to the issue much easier - the screenshot shows the firmware loaded is "sy3p", which is for 3-Phase Symmetra UPS - so the card is complaining because it's trying to speak to a Symmetra, and a Symmetra isn't answering.

 

The current firmware for your UPS would be https://www.se.com/ie/en/product/SFSUMX704/ups-network-management-card-v7-0-4-firmware-for-smartups-...

 

As the card still appears to be on the network, recovery should be as simple as loading the correct firmware.

 

Regards,

  Shaun

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

NikSpasov
Crewman NikSpasov
Crewman

Posted: ‎2022-01-17 10:51 AM . Last Modified: ‎2022-01-18 12:07 AM

In response to Shaun
0 Likes
1
4568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-17 10:51 AM . Last Modified: ‎2022-01-18 12:07 AM

Thank you very much, @Shaun,

Somehow, I successfully killed the network card.

 

I have downloaded this: file apc_hw05_aos704_sumx704_bootmon109.exe
In the middle of installation, the tool lost connection to UPS. (FTP method)

Now I can't find the network card anymore.

 

Do you have any idea how to fix this mess?

 

Thanks

Nik

 

  • Tags:
  • @Shaun
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

NikSpasov
Crewman NikSpasov
Crewman

Posted: ‎2022-01-18 02:08 AM

In response to NikSpasov
0 Likes
0
4553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-18 02:08 AM

Hi @Shaun ,

Everything is fine now. 

The new firmware has disabled HTTP communication. HTTPS is enabled and now all works fine.

Thank you very much!

All the best,

Nik

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jozef.79
Jozef.79
Cadet

Posted: ‎2023-12-22 02:15 PM

0 Likes
0
2907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-12-22 02:15 PM

Where its possible download prev. versions of firmware? I update to 7.1.2, and I got same trouble Lost Communication to the UPS...

thanks a lot 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore