Local Management-To-UPS Communication Lost

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Local Management-To-UPS Communication Lost
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:49 AM . Last Modified: ‎2024-03-07 02:33 AM

0 Likes
13
3939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:49 AM . Last Modified: ‎2024-03-07 02:33 AM

Local Management-To-UPS Communication Lost

I have Smart-UPS RT 3000 XL and KI am start receiving messages related to Lost the local network management interface-to-UPS communication.

Every 3 minutes A message is sent

However I am able to access the devices using the web interface trough the ip.

Anyone has the same issue?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • network
  • snmp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

can you please follow [these instructions|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=9321] to download your event.txt file on your network management card? we need to see the event log to determine what may be happening to cause these messages to come up. please post/attach the text file here if possible.

also, it would be helpful to know if you have anything attached to the serial port on this UPS even though you are using the network management card.

thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:33 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:33 AM

I have Smart-UPS RT 3000 XL and KI am start receiving messages related to Lost the local network management interface-to-UPS communication.

Every 3 minutes A message is sent

However I am able to access the devices using the web interface trough the ip.

Anyone has the same issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:33 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:33 AM

no problem. just keep an eye on it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:33 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:33 AM

Attached is the event.txt file. Thanks in advance for the help

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:33 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:33 AM

the file i gave you (for the firmware upgrade) is an upgrade wizard where you just have to answer a couple of prompts, noted in the kbase Techie provided.

at the time you pulled the config.ini file, the network management card was not communicating with the UPS. when you login to the network management card, which we know itself is online, and click on the UPS tab, do you EVER see any data displayed there? i imagine you do because you are seeing UPS type events in the event log but I just want to double check.

i need a config.ini file pulled when the network card is talking with the UPS and displaying data if possible.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:33 AM

0 Likes
0
3925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:33 AM

Heres the Information of the unit:
Model Number: AP9619
Serial Number: BA0843018558
Hardware Revision: A10
Manufacture Date: 10/24/2008
MAC Address: 00 C0 B7 D4 5D 7A
Management Uptime: 46 Days 23 Hours 57 Minutes

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

Click on the below link to find the instructions on how to upgrade the firmware of the NMC.
[http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=768]

Secondly, the model number(AP9619) which you proivided is the NMC part number not the UPS model number. Could you please have a look at the rear of the UPS to find the exact model number of the UPS on a white bar code sticker?

I hope that this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

I was able to access the device but at the UPS tab no information was shown.
After the firmware upgrade the devices were responding again and the UPS tab information was shown again. Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

I am having the same problem.
I have downloaded the files as discussed.
Would someone be prepared to read the files, and recommend a course of action.
Thanks

Nigel

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

hi

can you please give me the exact model of the UPS that this is installed in? it will be on the back or bottom of the UPS on a little white sticker.

also, you are two firmware revisions behind so you could certainly upgrade to take advantage of enhancements and bug fixes.

your messages appear to be the result of warmstarts. [you can read what that means here|http://nam-en.apc.com/app/answers/detail/a_id/2572]. i'd recommend upgrading to the latest firmware revision to start (AOS 3.7.3/Smart UPS Matrix APP 3.7.2) and then checking the items on the list to rule them out. you could temporarily change your default gateway to another valid node on your network to ensure that you do not have an issue with network traffic.

it seems unprovoked so if it is not network traffic and difficulty reaching the default gateway, it may one of the firmware issues mentioned in the article above.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

no problem. ultimately, APC support needs to be contacted if it is an SURTD3000XLI.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

can you let me know what model UPS that this is? based on the info i can see in the files, it appears your issue may be related to SURTD3000XLI unit - please see the [issue described here|http://nam-en.apc.com/app/answers/detail/a_id/10891/] that explains what you need to do.

if it is not an SURTD3000XLI, please let me know the model of UPS so i can give you some more steps to try. thanks!!

Reply

Link copied. Please paste this link to share this article on your social media post.

rstoyanov_apc
rstoyanov_apc
Cadet

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

0 Likes
0
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

Hi,
thanks for your quick answer . Yes it is a SURTD3000XLI. I just contact my vendor and wait for answer.

Thanks one more time

:)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

0 Likes
0
3939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:50 AM . Last Modified: ‎2024-03-07 02:32 AM

can you please follow [these instructions|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=9321] to download your event.txt file on your network management card? we need to see the event log to determine what may be happening to cause these messages to come up. please post/attach the text file here if possible.

also, it would be helpful to know if you have anything attached to the serial port on this UPS even though you are using the network management card.

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore