Local Management-To-NMC Integrated EM Sensor Communication Lost: Universal I/O at Port 1-2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Local Management-To-NMC Integrated EM Sensor Communication Lost: Universal I/O at Port 1-2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
UPSSupport
UPSSupport
Cadet

Posted: ‎2022-09-17 10:41 AM . Last Modified: ‎2022-09-17 10:47 AM

0 Likes
2
1543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-17 10:41 AM . Last Modified: ‎2022-09-17 10:47 AM

Local Management-To-NMC Integrated EM Sensor Communication Lost: Universal I/O at Port 1-2

 
Firmware upgrade to v7.x causes event log to fill up every second with the following errors.
 
 09/17/202213:29:51DeviceEnvironment: Lost the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 2) communication.
 09/17/202213:29:51DeviceEnvironment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 2) communication.
 09/17/202213:29:50DeviceEnvironment: Lost the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication.
 09/17/202213:29:50DeviceEnvironment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication.
 
This is affecting the cards performance, interface is slow to respond to all requests.
 
Model Number
AP9631
Serial Number
5A1522T13462
Hardware Revision
05
Manufacture Date
05/30/2015
 
Application Module
Name
sumx
Version
v7.0.8
Date
Jun 29 2022
APC OS (AOS)
Name
aos
Version
v7.0.8
Date
May 27 2022
APC Boot Monitor
Name
bootmon
Version
v1.0.9
Date
Mar 27 2019
 
Card is installed in an SMX1500RM2UNC
 
Have a pair of these UPS and AP9631 exact same hardware specs, both at the same firmware revisions, only the one card is having issues.
 
What I have done so far.
Various resets of the card - issue remains
BM>factory_reset - issue remains
reflash card with BM>xmodem
Rolled back to firmware version 6.5 - issue is gone
Rolled back to various 7.x versions - issue remains.
removed for an extended period of time and reseated the card
installed environment monitor cables, reset lost com alarm, reboot
 
Hopefully someone has some insight into this issue, as I can no longer use my environment monitors with the card in this state.
 
Thanks All for your input
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-09-25 04:09 PM

0 Likes
1
1474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-25 04:09 PM

Hi @UPSSupport 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  Apologies for the inconvenience that the issue has caused.

 

I would normally disconnect everything that is connected to the network card and press the reset button quickly to reboot the NMC or reseat it.  Once it has booted up, I will then start connecting those peripherals back to the card and reboot it once more.

 

If possible, I also suggest reflashing the card once more.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

UPSSupport
UPSSupport
Cadet

Posted: ‎2022-11-25 05:28 PM . Last Modified: ‎2022-11-25 05:29 PM

In response to JonPro
0 Likes
0
1423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-25 05:28 PM . Last Modified: ‎2022-11-25 05:29 PM

Hi,

 

Have done the reflash and the reset and the reseat.

 

There are no sensors/peripherals connected to the card.

There never was, except for a test to reset the fault.

 

I want to connect sensors to it, but those i/o ports are in a fault state.

 

the errors every few seconds make the card almost unusable, as it consumes lots of resources recording faults continually.

 

Have picked up a replacement card, but would like to revive this one for another unit for environment monitoring.

 

thanks for the follow up.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore