Smart-UPS 10KW Batteries last two years at best

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 10KW Batteries last two years at best
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2022-10-25 08:48 AM

0 Likes
6
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-25 08:48 AM

Smart-UPS 10KW Batteries last two years at best

I have an old apc smart-ups RT 10kw system that's been running fine for many years. It still seems to have life left so I keep it in use.

 

The problem is that it needs new batteries every couple of years, all 32 of them.

What's odd is that the UPS might get used 2 or 3 times in a couple of years and it's only for two minutes at a time because there is a generator that kicks in.

 

Does this sound normal to anyone else using these?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
mikeinnyc
Ensign mikeinnyc
Ensign

Posted: ‎2022-11-10 09:07 AM

0 Likes
5
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-10 09:07 AM

Just replaced my 16x batteries with 5k series. I did a complete run-down test and timed it. I was at "3 minutes exactly" with the stock batteries which was not enough time. My APC screen gave me a different run-down expectancy which was wrong. These batteries lasted 5 years.

 

New replacements 16 replacement batteries gave me 6 minutes 42 seconds at 50 % load. Since I have my generator outside this is just enough time. No need for me to load up on expensive batteries when my Generator is ready to go.

 

Honestly, get the battery sized to the generator run time plus 20 percent. I'll take good old fossil fuel to lead acid batteries any day.

Whatever you don't recondition the sealed lead acid batteries like on youtube. Remember, this is going inside a living space. Hope this helps.

 

  • Tags:
  • AGM Batteries
  • english
  • lead acid battery
Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2022-11-10 09:39 AM

In response to mikeinnyc
0 Likes
4
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-10 09:39 AM

Well, it's interesting input but no, it doesn't help to know why the batteries only last a couple years.

As I mentioned, I too have a generator which comes on 60 seconds after a power failure so at most, the UPS sees a load for that amount of time, maybe 2-3 times a year. I've never seen the batteries get depleted because the geny comes on.

 

So I'm still in the dark on why the batteries don't last longer.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Guinea_Pig
Ensign Guinea_Pig
Ensign

Posted: ‎2022-11-17 06:17 AM

In response to mlewis_apc
0 Likes
3
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-17 06:17 AM

Check the battery temperature (if the UPS has an NMC installed this will tell you) - anything over 25C will degrade overall battery life.  Temperature is the most common cause of short life.

 

The way the batteries are charged can also seriously effect the life of the battery.  High current ripple or high voltage from the charger can be an issue, however in this case I doubt that the UPS charger could fail in such a way as to cause this issue without having some sort of alarm.

 

In my experience it is always a heat / ventilation issue on SRT UPS so it would be interesting if this is different.

 

Set the battery test period up (if it has one - depends on the exact SRT model I think) to give the batteries some "exercise"

 

Regards

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2022-11-17 01:33 PM . Last Modified: ‎2022-11-17 01:34 PM

In response to Guinea_Pig
0 Likes
2
1562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-17 01:33 PM . Last Modified: ‎2022-11-17 01:34 PM

Unfortunately, heat would not be an issue either. It's installed in a small equipment room that has good ventilation. Ambient temps never get higher than 78. Fans and AC automatically kick in.

 

It seems there is not going to be a way to know why but it's worrying me about buying any more of these large UPS's. I also have a number of 3KW ones that have never shown such problems.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

mikeinnyc
Ensign mikeinnyc
Ensign

Posted: ‎2022-11-26 12:04 PM

In response to mlewis_apc
0 Likes
1
1478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-26 12:04 PM

sulfation.jpeg

 

 

Law of physics - This is a chemical reaction where the plates eventually become sulfated.

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2022-11-27 07:26 AM

In response to mikeinnyc
0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-27 07:26 AM

That's great info but doesn't answer my question :).

No reason at all batteries should die in two years barely being used. They should last at least 3-4 years like all my other APC backup devices do.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore