Posted: 2022-09-17 10:41 AM . Last Modified: 2022-09-17 10:47 AM
Local Management-To-NMC Integrated EM Sensor Communication Lost: Universal I/O at Port 1-2
09/17/2022 | 13:29:51 | Device | Environment: Lost the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 2) communication. |
09/17/2022 | 13:29:51 | Device | Environment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 2) communication. |
09/17/2022 | 13:29:50 | Device | Environment: Lost the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication. |
09/17/2022 | 13:29:50 | Device | Environment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication. |
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-25 04:09 PM
Hi @UPSSupport
Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. Apologies for the inconvenience that the issue has caused.
I would normally disconnect everything that is connected to the network card and press the reset button quickly to reboot the NMC or reseat it. Once it has booted up, I will then start connecting those peripherals back to the card and reboot it once more.
If possible, I also suggest reflashing the card once more.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-25 05:28 PM . Last Modified: 2022-11-25 05:29 PM
Hi,
Have done the reflash and the reset and the reseat.
There are no sensors/peripherals connected to the card.
There never was, except for a test to reset the fault.
I want to connect sensors to it, but those i/o ports are in a fault state.
the errors every few seconds make the card almost unusable, as it consumes lots of resources recording faults continually.
Have picked up a replacement card, but would like to revive this one for another unit for environment monitoring.
thanks for the follow up.