Line Minimum: Not found VAC --- in my Debian lenny Server
  • Line Minimum: Not found VAC --- in my Debian lenny Server
Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM
2742
{color:#0000ff}*ALL My UPS Status*{color}
APC : 001,042,1026
DATE : Tue Aug 24 15:52:42 CST 2010
HOSTNAME : ipb
RELEASE : 3.14.4
VERSION : 3.14.4 (18 May 2008) debian
UPSNAME : ipb
CABLE : USB Cable
MODEL : Smart-UPS 1000
UPSMODE : Stand Alone
STARTTIME: Tue Aug 24 15:17:18 CST 2010
STATUS : ONLINE
LINEV : 115.2 Volts
LOADPCT : 13.6 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 117.0 Minutes
MBATTCHG : 15 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
OUTPUTV : 115.9 Volts
SENSE : High
DWAKE : -01 Seconds
DSHUTD : 090 Seconds
LOTRANS : 106.0 Volts
HITRANS : 127.0 Volts
RETPCT : 000.0 Percent
ITEMP : 31.5 C Internal
ALARMDEL : No alarm
BATTV : 27.4 Volts
LINEFREQ : 60.0 Hz
LASTXFER : Automatic or explicit self test
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x07000008 Status Flag
SERIALNO : AS0946231630
BATTDATE : 2009-11-12
NOMOUTV : 120 Volts
NOMBATTV : 24.0 Volts
FIRMWARE : 652.18.D USB FW:7.4
APCMODEL : Smart-UPS 1000
END APC : Tue Aug 24 15:53:16 CST 2010
Not found:
MAXLINEV : ??? Volts
MINLINEV : ??? Volts
Why?
On the APCUPSD UPS Network Monitor page >> Local Host
Line Maximum: Not found VAC
Thanks.
apcupsd.conf
## apcupsd.conf v1.1 ##
# for apcupsd release 3.14.4 (18 May 2008) - debian
# "apcupsd" POSIX config file
# ========= General configuration parameters ============
# UPSNAME xxx
# Use this to give your UPS a name in log files and such. This
# is particulary useful if you have multiple UPSes. This does not
# set the EEPROM. It should be 8 characters or less.
#UPSNAME
# UPSCABLE
# Defines the type of cable connecting the UPS to your computer.
# Possible generic choices for are:
# simple, smart, ether, usb
# Or a specific cable model number may be used:
# 940-0119A, 940-0127A, 940-0128A, 940-0020B,
# 940-0020C, 940-0023A, 940-0024B, 940-0024C,
# 940-1524C, 940-0024G, 940-0095A, 940-0095B,
# 940-0095C, M-04-02-2000
UPSCABLE usb
# To get apcupsd to work, in addition to defining the cable
# above, you must also define a UPSTYPE, which corresponds to
# the type of UPS you have (see the Description for more details).
# You must also specify a DEVICE, sometimes referred to as a port.
# For USB UPSes, please leave the DEVICE directive blank. For
# other UPS types, you must specify an appropriate port or address.
# UPSTYPE DEVICE Description
# apcsmart /dev/tty** Newer serial character device,
# appropriate for SmartUPS models using
# a serial cable (not USB).
# usb Most new UPSes are USB. A blank DEVICE
# setting enables autodetection, which is
# the best choice for most installations.
# net hostname:port Network link to a master apcupsd
# through apcupsd's Network Information
# Server. This is used if you don't have
# a UPS directly connected to your computer.
# snmp hostname:port:vendor:community
# SNMP Network link to an SNMP-enabled
# UPS device. Vendor is the MIB used by
# the UPS device: can be "APC", "APC_NOTRAP"
# or "RFC" where APC is the powernet MIB,
# "APC_NOTRAP" is powernet with SNMP trap
# catching disabled, and RFC is the IETF's
# rfc1628 UPS-MIB. You usually want "APC".
# Port is usually 161. Community is usually
# "private".
# dumb /dev/tty** Old serial character device for use
# with simple-signaling UPSes.
# pcnet ipaddr:username:passphrase
# PowerChute Network Shutdown protocol
# which can be used as an alternative to SNMP
# with AP9617 family of smart slot cards.
# ipaddr is the IP address of the UPS mgmt
# card. username and passphrase are the
# credentials for which the card has been
# configured.
#UPSTYPE apcsmart
#DEVICE /dev/ttyS0
UPSTYPE usb
DEVICE
# POLLTIME
# Interval (in seconds) at which apcupsd polls the UPS for status. This
# setting applies both to directly-attached UPSes (UPSTYPE apcsmart, usb,
# dumb) and networked UPSes (UPSTYPE net, snmp). Lowering this setting
# will improve apcupsd's responsiveness to certain events at the cost of
# higher CPU utilization. The default of 60 is appropriate for most
# situations.
#POLLTIME 60
# LOCKFILE
# Path for device lock file. Not used on Win32.
LOCKFILE /var/lock
# SCRIPTDIR
# Directory in which apccontrol and event scripts are located.
SCRIPTDIR /etc/apcupsd
# PWRFAILDIR
# Directory in which to write the powerfail flag file. This file
# is created when apcupsd initiates a system shutdown and is
# checked in the OS halt scripts to determine if a killpower
# (turning off UPS output power) is required.
PWRFAILDIR /etc/apcupsd
# NOLOGINDIR
# Directory in which to write the nologin file. The existence
# of this flag file tells the OS to disallow new logins.
NOLOGINDIR /etc
# ======== Configuration parameters used during power failures ==========
# The ONBATTERYDELAY is the time in seconds from when a power failure
# is detected until we react to it with an onbattery event.
# This means that, apccontrol will be called with the powerout argument
# immediately when a power failure is detected. However, the
# onbattery argument is passed to apccontrol only after the
# ONBATTERYDELAY time. If you don't want to be annoyed by short
# powerfailures, make sure that apccontrol powerout does nothing
# i.e. comment out the wall.
ONBATTERYDELAY 6
# Note: BATTERYLEVEL, MINUTES, and TIMEOUT work in conjunction, so
# the first that occurs will cause the initation of a shutdown.
# If during a power failure, the remaining battery percentage
# (as reported by the UPS) is below or equal to BATTERYLEVEL,
# apcupsd will initiate a system shutdown.
#BATTERYLEVEL 5
#BATTERYLEVEL 95
BATTERYLEVEL 15
# If during a power failure, the remaining runtime in minutes
# (as calculated internally by the UPS) is below or equal to MINUTES,
# apcupsd, will initiate a system shutdown.
MINUTES 3
# If during a power failure, the UPS has run on batteries for TIMEOUT
# many seconds or longer, apcupsd will initiate a system shutdown.
# A value of 0 disables this timer.
# Note, if you have a Smart UPS, you will most likely want to disable
# this timer by setting it to zero. That way, you UPS will continue
# on batteries until either the % charge remaing drops to or below BATTERYLEVEL,
# or the remaining battery runtime drops to or below MINUTES. Of course,
# if you are testing, setting this to 60 causes a quick system shutdown
# if you pull the power plug.
# If you have an older dumb UPS, you will want to set this to less than
# the time you know you can run on batteries.
TIMEOUT 0
# Time in seconds between annoying users to signoff prior to
# system shutdown. 0 disables.
#ANNOY 300
ANNOY 60
# Initial delay after power failure before warning users to get
# off the system.
ANNOYDELAY 60
# The condition which determines when users are prevented from
# logging in during a power failure.
# NOLOGON [ disable | timeout | percent | minutes | always ]
NOLOGON disable
# If KILLDELAY is non-zero, apcupsd will continue running after a
# shutdown has been requested, and after the specified time in
# seconds attempt to kill the power. This is for use on systems
# where apcupsd cannot regain control after a shutdown.
# KILLDELAY 0 disables
KILLDELAY 0
# ==== Configuration statements for Network Information Server ====
# NETSERVER [ on | off ] on enables, off disables the network
# information server. If netstatus is on, a network information
# server process will be started for serving the STATUS and
# EVENT data over the network (used by CGI programs).
NETSERVER on
# NISIP
# IP address on which NIS server will listen for incoming connections.
# This is useful if your server is multi-homed (has more than one
# network interface and IP address). Default value is 0.0.0.0 which
# means any incoming request will be serviced. Alternatively, you can
# configure this setting to any specific IP address of your server and
# NIS will listen for connections only on that interface. Use the
# loopback address (127.0.0.1) to accept connections only from the
# local machine.
NISIP 127.0.0.1
# NISPORT default is 3551 as registered with the IANA
# port to use for sending STATUS and EVENTS data over the network.
# It is not used unless NETSERVER is on. If you change this port,
# you will need to change the corresponding value in the cgi directory
# and rebuild the cgi programs.
NISPORT 3551
# If you want the last few EVENTS to be available over the network
# by the network information server, you must define an EVENTSFILE.
EVENTSFILE /var/log/apcupsd.events
# EVENTSFILEMAX
# By default, the size of the EVENTSFILE will be not be allowed to exceed
# 10 kilobytes. When the file grows beyond this limit, older EVENTS will
# be removed from the beginning of the file (first in first out). The
# parameter EVENTSFILEMAX can be set to a different kilobyte value, or set
# to zero to allow the EVENTSFILE to grow without limit.
EVENTSFILEMAX 10
# ========== Configuration statements used if sharing =============
# a UPS with more than one machine
# Remaining items are for ShareUPS (APC expansion card) ONLY
# UPSCLASS [ standalone | shareslave | sharemaster ]
# Normally standalone unless you share an UPS using an APC ShareUPS
# card.
UPSCLASS standalone
# UPSMODE [ disable | share ]
# Normally disable unless you share an UPS using an APC ShareUPS card.
UPSMODE disable
# ===== Configuration statements to control apcupsd system logging ========
# Time interval in seconds between writing the STATUS file; 0 disables
STATTIME 0
# Location of STATUS file (written to only if STATTIME is non-zero)
STATFILE /var/log/apcupsd.status
# LOGSTATS [ on | off ] on enables, off disables
# Note! This generates a lot of output, so if
# you turn this on, be sure that the
# file defined in syslog.conf for LOG_NOTICE is a named pipe.
# You probably do not want this on.
LOGSTATS off
# Time interval in seconds between writing the DATA records to
# the log file. 0 disables.
DATATIME 0
# FACILITY defines the logging facility (class) for logging to syslog.
# If not specified, it defaults to "daemon". This is useful
# if you want to separate the data logged by apcupsd from other
# programs.
#FACILITY DAEMON
# ========== Configuration statements used in updating the UPS EPROM =========
# These statements are used only by apctest when choosing "Set EEPROM with conf
# file values" from the EEPROM menu. THESE STATEMENTS HAVE NO EFFECT ON APCUPSD.
# UPS name, max 8 characters
#UPSNAME UPS_IDEN
# Battery date - 8 characters
#BATTDATE mm/dd/yy
# Sensitivity to line voltage quality (H cause faster transfer to batteries)
# SENSITIVITY H M L (default = H)
#SENSITIVITY H
# UPS delay after power return (seconds)
# WAKEUP 000 060 180 300 (default = 0)
#WAKEUP 60
# UPS Grace period after request to power off (seconds)
# SLEEP 020 180 300 600 (default = 20)
#SLEEP 180
# Low line voltage causing transfer to batteries
# The permitted values depend on your model as defined by last letter
# of FIRMWARE or APCMODEL. Some representative values are:
# D 106 103 100 097
# M 177 172 168 182
# A 092 090 088 086
# I 208 204 200 196 (default = 0 => not valid)
#LOTRANSFER 208
# High line voltage causing transfer to batteries
# D 127 130 133 136
# M 229 234 239 224
# A 108 110 112 114
# I 253 257 261 265 (default = 0 => not valid)
#HITRANSFER 253
# Battery charge needed to restore power
# RETURNCHARGE 00 15 50 90 (default = 15)
#RETURNCHARGE 15
# Alarm delay
# 0 = zero delay after pwr fail, T = power fail + 30 sec, L = low battery, N = never
# BEEPSTATE 0 T L N (default = 0)
#BEEPSTATE T => This is default.
BEEPSTATE N
# Low battery warning delay in minutes
# LOWBATT 02 05 07 10 (default = 02)
LOWBATT 05
# UPS Output voltage when running on batteries
# D 115
# M 208
# A 100
# I 230 240 220 225 (default = 0 => not valid)
#OUTPUTVOLTS 230
# Self test interval in hours 336=2 weeks, 168=1 week, ON=at power on
# SELFTEST 336 168 ON OFF (default = 336)
# SELFTEST 336
Message was edited by: aeolus
  • apcupsd.conf
2742
APC : 001,042,1026
HOSTNAME : ipb
RELEASE : 3.14.4
UPSNAME : ipb
CABLE : USB Cable
STATUS : ONLINE
LINEV : 115.2 Volts
MAXTIME : 0 Seconds
SENSE : High
DWAKE : -01 Seconds
ALARMDEL : No alarm
BATTV : 27.4 Volts
LINEFREQ : 60.0 Hz
NUMXFERS : 0
TONBATT : 0 seconds
XOFFBATT : N/A
SELFTEST : NO
NOMOUTV : 120 Volts
Not found:
Why?
Thanks.
apcupsd.conf
# UPSNAME xxx
#UPSNAME
# UPSCABLE
UPSCABLE usb
# "private".
# configured.
#UPSTYPE apcsmart
#DEVICE /dev/ttyS0
UPSTYPE usb
DEVICE
# POLLTIME
# situations.
#POLLTIME 60
# LOCKFILE
LOCKFILE /var/lock
# SCRIPTDIR
# PWRFAILDIR
# NOLOGINDIR
NOLOGINDIR /etc
ONBATTERYDELAY 6
#BATTERYLEVEL 5
#BATTERYLEVEL 95
BATTERYLEVEL 15
MINUTES 3
TIMEOUT 0
#ANNOY 300
ANNOY 60
# off the system.
ANNOYDELAY 60
NOLOGON disable
KILLDELAY 0
NETSERVER on
# NISIP
# local machine.
NISIP 127.0.0.1
NISPORT 3551
# EVENTSFILEMAX
EVENTSFILEMAX 10
# card.
UPSCLASS standalone
UPSMODE disable
STATTIME 0
LOGSTATS off
DATATIME 0
# programs.
#FACILITY DAEMON
#UPSNAME UPS_IDEN
#BATTDATE mm/dd/yy
#SENSITIVITY H
#WAKEUP 60
#SLEEP 180
# D 106 103 100 097
# M 177 172 168 182
# A 092 090 088 086
#LOTRANSFER 208
# D 127 130 133 136
# M 229 234 239 224
# A 108 110 112 114
#HITRANSFER 253
#RETURNCHARGE 15
# Alarm delay
BEEPSTATE N
LOWBATT 05
# D 115
# M 208
# A 100
#OUTPUTVOLTS 230
# SELFTEST 336
Replies 4
Thanks for your useful information.
2743
APC : 001,042,1026
HOSTNAME : ipb
RELEASE : 3.14.4
UPSNAME : ipb
CABLE : USB Cable
STATUS : ONLINE
LINEV : 115.2 Volts
MAXTIME : 0 Seconds
SENSE : High
DWAKE : -01 Seconds
ALARMDEL : No alarm
BATTV : 27.4 Volts
LINEFREQ : 60.0 Hz
NUMXFERS : 0
TONBATT : 0 seconds
XOFFBATT : N/A
SELFTEST : NO
NOMOUTV : 120 Volts
Not found:
Why?
Thanks.
apcupsd.conf
# UPSNAME xxx
#UPSNAME
# UPSCABLE
UPSCABLE usb
# "private".
# configured.
#UPSTYPE apcsmart
#DEVICE /dev/ttyS0
UPSTYPE usb
DEVICE
# POLLTIME
# situations.
#POLLTIME 60
# LOCKFILE
LOCKFILE /var/lock
# SCRIPTDIR
# PWRFAILDIR
# NOLOGINDIR
NOLOGINDIR /etc
ONBATTERYDELAY 6
#BATTERYLEVEL 5
#BATTERYLEVEL 95
BATTERYLEVEL 15
MINUTES 3
TIMEOUT 0
#ANNOY 300
ANNOY 60
# off the system.
ANNOYDELAY 60
NOLOGON disable
KILLDELAY 0
NETSERVER on
# NISIP
# local machine.
NISIP 127.0.0.1
NISPORT 3551
# EVENTSFILEMAX
EVENTSFILEMAX 10
# card.
UPSCLASS standalone
UPSMODE disable
STATTIME 0
LOGSTATS off
DATATIME 0
# programs.
#FACILITY DAEMON
#UPSNAME UPS_IDEN
#BATTDATE mm/dd/yy
#SENSITIVITY H
#WAKEUP 60
#SLEEP 180
# D 106 103 100 097
# M 177 172 168 182
# A 092 090 088 086
#LOTRANSFER 208
# D 127 130 133 136
# M 229 234 239 224
# A 108 110 112 114
#HITRANSFER 253
#RETURNCHARGE 15
# Alarm delay
BEEPSTATE N
LOWBATT 05
# D 115
# M 208
# A 100
#OUTPUTVOLTS 230
# SELFTEST 336
CSM
CSM
Cadet
Posted: ‎2022-01-30 05:23 AM
In response to Anonymous user
2663
I’m having similar issue, and not clear from earlier response what the solution is to display the Line Minimum and Maximum.
Posted: ‎2022-02-01 06:32 AM
In response to CSM
@CSM
The minimum and maximum voltage readings (Vmin/Vmax) do not get transmitted from the UPS when connected with a Smart-UPS via USB cable. These values are filled in when the SUA model UPS is connected via the 940-0024C or 940-1524C serial communications cable. This is a limitation of USB communications on a Smart-UPS model UPS. The current voltage at the time the data is being recorded does populate with the correct information.
Also, the The minimum and maximum voltage readings (Vmin/Vmax) do not get posted to when attached to
SMX, SMT, SMTL, SMC, SRTL, SRT, SURTD, SCL Smart-UPS.