Limiting which IP can initiate a UPS shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Limiting which IP can initiate a UPS shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:17 AM

0 Likes
7
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:17 AM

Limiting which IP can initiate a UPS shutdown

Hello All!

In our rack we have several servers and a single UPS, this is a hypothetical configuration.

How can we configure.....or get........the UPS to only respond to a "Shutdown UPS after shutdown" from a single designated machine.

Example, say that we have five physical machines running several hundred virtual machines. As we add and remove machines, it would be very easy to forget to uncheck the "Shutdown UPS after shutdown" which could cause a single virtual machine to drop several hundred machines.

What is the best way to prevent this....it would be nice if I could get the UPS to only recognize a designated machine as the authoritative machine. Can ISX Manager help.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:16 AM

0 Likes
0
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:16 AM

Hello All!

In our rack we have several servers and a single UPS, this is a hypothetical configuration.

How can we configure.....or get........the UPS to only respond to a "Shutdown UPS after shutdown" from a single designated machine.

Example, say that we have five physical machines running several hundred virtual machines. As we add and remove machines, it would be very easy to forget to uncheck the "Shutdown UPS after shutdown" which could cause a single virtual machine to drop several hundred machines.

What is the best way to prevent this....it would be nice if I could get the UPS to only recognize a designated machine as the authoritative machine. Can ISX Manager help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:17 AM

0 Likes
0
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:17 AM

If this is something that must be accomplished, and must not rely on one of a hundred techs to remember special conditions such as who is the last man standing box and remember you must always uncheck the box at install........do I have some creative alternatives here, alternate control processes or products that I can purchase to assist.

Ideas...modified APC firmware that can never be shut down remotely.....modified APC installer software that does not have that check box checked by default......third party monitoring software.......a router in the middle that eats the shut down packet unless initiated by a specific IP address.....????........do I have any options, even creative options or options that cost money.....?

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:17 AM

0 Likes
0
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:17 AM

Unless you have a configured event to shutdown in the PCNS interface, the PCNS client is set to shutdown when the UPS has reached low battery signal time. Therefore, if you leave it like that, all of your servers/workstations will shutdown when the UPS has reached its low battery signal time. In essence, you're letting the UPS run on battery for as long as possible, not doing a sequenced shutdown, and not powering off the UPS after the shutdowns have completed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:17 AM

0 Likes
0
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:17 AM

Hello,

You can always perform a silent installation. Install PCNS on a machine, configure it as you please, in this case make sure that the checkbox to shutdown UPS is unchecked. Doing it this way will allow you to install PCNS on multiple computers with the same configuration.


More information can be found at:

http://www.apcmedia.com/salestools/ASTE-6Z5QEQ_R0_EN.pdf

Please note that this is not a MASS software installation. These instructions will not push the PCNS clients to your machines. It will simply allow you to install the PCNS client with the same configuration on multiple machines. Please read the document carefully.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:17 AM

0 Likes
0
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:17 AM

I saw that you mentioned virtual machine. You don't need to install PCNS on all the virtual machines, only on the ESX server itself. When you shutdown the physical box, it will gracefully shutdown the virtual machines.

Please see below:

http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8669&p_created=1182929348&p...

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:16 AM

0 Likes
0
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:16 AM

Is this an installation on an ESX server? If so, there is no need to install the software on all of the virtual machines. If you set it up to shutdown the ESX server, the ESX server will shutdown client operating systems. Here is kbase doc:

http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8669&p_created=1182929348&p...

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:16 AM

0 Likes
0
863
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:16 AM

Thanks for the replies.....yest this is an ESX setup, along with many physical servers.
I was not aware of the new integration with ESX, so I will look further in to that.

Still, on the physical side of things, I am guessing that their is no way to designate a master or authoritative computer to control the shut down of the UPS.....that the UPS will take the shut down command from any registered client. Is that about right?

Thanks for the input,
Kevin

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:16 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:16 AM

Hello All!

In our rack we have several servers and a single UPS, this is a hypothetical configuration.

How can we configure.....or get........the UPS to only respond to a "Shutdown UPS after shutdown" from a single designated machine.

Example, say that we have five physical machines running several hundred virtual machines. As we add and remove machines, it would be very easy to forget to uncheck the "Shutdown UPS after shutdown" which could cause a single virtual machine to drop several hundred machines.

What is the best way to prevent this....it would be nice if I could get the UPS to only recognize a designated machine as the authoritative machine. Can ISX Manager help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of