Cancel shutdown process when power is back
  • Cancel shutdown process when power is back
5060
142
Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:17 AM
1112
I'm trying to figure if possible to crate option, if power is off - the UPS start the shutting down process, and let's say it planned to happen in 5 minuets, after 3 minutes the power is back again, as i see now the shutting down process will continue till it turned off then power on again.
There is any solution for that?
I'm using PowerChute Business Edition with APC Smart UPS 3KVA
Thank you
Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:16 AM
Thank you Bill!
You can configure PowerChute to start the shutdown process after the UPS has run on the battery for 5 minutes. If AC is restored after only running on battery for 3 minutes, the shutdown process will not begin.
Once PowerChute commands the OS down, the process should complete preventing OS corruption.
Thank you Bill!